Discuss 1mm T&E on a 16A MCB - doesn't look or feel right! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
362
Doing an EICR, one circuit described as Central Heating with 1 mm T&E cable connected but on a 16A MCB. When I look closer it appears an Immersion heater has been tagged onto the circuit!

I've not been able to ascertain the cable route and its installation method. This is a single storey extension, no loft space.

If I use Ref C then 1mm is OK (just). There is no signs of overheating at either end of the cable, insulation measurements are good. The immersion is probably seldom used (if at all) because of a boiler in use.

I guess I can't give it an Observation unless I chose another installation method.

Any comments/advice?
 
If it's only feeding a central heating system then if it's connected through a switch fused spur the cable on the load side will be fused down to 3amps hopefully.
It will never pull 16amps so overload protection can be omitted plus the 3amp fuse will provide protection to the outgoing cable to the boiler.
If it's powering an immersion heater than yeah , wouldn't be happy with 16amp mcb feeding 1mm.
Cable is rated to 16amps clipped direct tho.
 
Think the norm is installing 2.5mm from db on 16amp mcb through a double pole switch and 1.5mm heat resistant flex out into immersion element
 
To be fair as well a typical immersion heater is 3000 watts so pulls 13amps.
The 16amp mcb won't need to provide overload protection to a fixed load so will only need to protect the cable for fault protection purposes.
 
I know I shouldn't be worrying about a solution, but the easiest way to resolve is to put the immersion on the ring! I do realise that its not recommended (not prohibited though) but as its not used much (if at all) I think this should be OK.
 
Table 52.3 in bs 7671 does say that power circuits are to be wired in 1.5mm as a minimum or for a specific appliance is specified by the product standard so depends on manufacturers instructions as well
 

Reply to 1mm T&E on a 16A MCB - doesn't look or feel right! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
608
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
852
I'm following a spark who used an existing Panel Heater circuit, for new gas boiler circuit 6 months ago. The panel heaters were removed, so it's...
Replies
43
Views
6K
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
633
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock