Discuss 1ph to 3 phase inverter in the UK Electrical Forum area at ElectriciansForums.net

stokielee

Trainee
Reaction score
12
I have been asked if I can wire a motor for a car lifter in a domestic garage, however the motor is 3 phase and only single phase is available in the property. Is it possible to use a single phase to 3 phase inverter to power this motor? I will attach photos of the motor and its output.
 

Attachments

  • 86a390e6-9c5f-4c68-b492-9ffd0f675460.jpeg
    221.6 KB · Views: 21
  • acd53a78-a9ba-4bba-a8e1-ba57ed2bd720.jpeg
    453.9 KB · Views: 21
short answer is yes.
however you will need to change the motor wiring from star to delta.
also the control circuit will need to be changed a little to accept 230v instead of 400v
it is not as easy to do as many people assume.
 
short answer is yes.
however you will need to change the motor wiring from star to delta.
also the control circuit will need to be changed a little to accept 230v instead of 400v
it is not as easy to do as many people assume.
Could you point in the right direction of what inverter I would need?

The wiring star to delta is pretty straight forward.
I will have to see about the control unit, hopefully it make more sense when I see it. Cheers
 
It's gonna be expensive to use a 230 single phase to 400v 3 phase inverter that's capable of supplying a 4kw AC3 motor load. Might be cheaper to just replace the motor with a 230v single phase type.
 
I have been asked if I can wire a motor for a car lifter in a domestic garage, however the motor is 3 phase and only single phase is available in the property. Is it possible to use a single phase to 3 phase inverter to power this motor? I will attach photos of the motor and its output.
I was going to say it is straightforward by using an inverter with single phase 230v input and 3 phase 230v output, and then connect the motor in delta. I've done this many times using Allen-Bradley Powerflex 4 series inverters, although less power rating than your application.
In delta, you will be looking for 17A/4kW 3 phase output and they don't appear to go that high. If you can find a manufacturer that makes one with that output, it should work.
 
No idea on the longevity but change the links to delta in the motor and use the below.

Link the run command in so as soon as it has power it will start to accelerate.

130 quid, job done.
 

Reply to 1ph to 3 phase inverter in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
374
Hi I have UPS 50KVA and the inverter output AC voltage is feeding a distribution panel 120/208 V 4 wires when I check UPS display it shows me...
Replies
1
Views
291
Hi I have inherited a compressor with a single phase motor but its been stripped and I need to fathom out what's what.. I don't know if it even...
Replies
13
Views
622
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Hi, As a DIYer I`ve quite a bit of wiring up domestic house single phase experience but no 3 phase experience. So I have been offered a two post...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top