Discuss 2 prong appliances with metal casing, are they safe to use ? in the UK Electrical Forum area at ElectriciansForums.net

ktnwin

DIY
Reaction score
15
I recently learned the importance of electrical grounding and checked all appliances in my home.
Toaster, Microwave oven have 3 prong power cord, so their metal casing would not cause any shock if the device has worn out connection inside. Some others like fans on the floor have only 2 prong and their casing is in plastic, no metal. These are safe to use IMHO.
However, I have some oil filled electric heaters with metallic fins and 2 prong power cords. These are still being sold in the market (Amazon for example). Are these safe to use ?
 
In the UK non-earthed appliances are Class II. These are generally plastic cased, but can have metal cases providing the requirements of double insulation (or equivalent reinforced insulation) are met. I'm not sure what the US regulations are, but we do have a few American members who may know.

Having said that, I've seen things purchased from various websites which have metal cases and no earths, but which are definitely NOT safe to use! Buyer beware if you are buying electrical items from random online sellers.
 
I recently learned the importance of electrical grounding and checked all appliances in my home.
Toaster, Microwave oven have 3 prong power cord, so their metal casing would not cause any shock if the device has worn out connection inside. Some others like fans on the floor have only 2 prong and their casing is in plastic, no metal. These are safe to use IMHO.
However, I have some oil filled electric heaters with metallic fins and 2 prong power cords. These are still being sold in the market (Amazon for example). Are these safe to use ?
In a sense yes they are safe only if they have a UL listing sticker on it
 
Megawatt, thanks for very clear answer. I never knew that the label UL on any electrical product means "safe to use". Make a lot of sense to me. My electric heaters do have that UL on the label.
 
Megawatt, thanks for very clear answer. I never knew that the label UL on any electrical product means "safe to use". Make a lot of sense to me. My electric heaters do have that UL on the label.
When you buy stuff online always make sure it is UL listed, if not don’t buy it and welcome to the forum
 

Reply to 2 prong appliances with metal casing, are they safe to use ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We're renovating our kitchen, and I have parts of the wall open and can rewire circuits right now if needed. We currently have three 20A circuits...
Replies
4
Views
1K
We built a retirement home in the Philippines and relocated here a little less than 2 years ago from Georgia, USA. My wife is a Filipina and owns...
Replies
0
Views
1K
If one of your coworkers suffers a severe electric shock, your first instinct will most likely be to rush to their rescue. But first, pause and...
Replies
2
Views
691
While adding come circuits to my garage I realized that some existing circuits were not done correctly. These are 240v 30 amp circuits to run...
Replies
1
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock