Discuss 2 switched lives for extractor? in the DIY Electrical Advice area at ElectriciansForums.net

jshailes

-
DIY
Reaction score
3
I currently have a 2 gang switch outside the bathroom - one for the light and one for the extractor:

Main Ceiling Light (1).png

I'd like to change the way it works slightly so that the extractor comes on if either the extractor switch is turned on or the light switch is turned on. I was wondering if anyone could offer any advice on if/how this is usually done?
 
I don’t see why you would want to wire it a different way? It’s perfect the way it is.
Independent switches so you can have light without fan for a quick visit to the loo, fan with light, for showering.... fan without light to clear the room without having the light on.

what you want is possible, but you would either need a double pole switch in place of the light switch, or a relay somewhere.

I’m going to start an argument with my esteemed colleagues and say the 3 core and earth to the 3 pole isolator has the wrong colours. Black should sleeved brown as switch and grey Should be sleeved blue as neutral (black and grey mixed up)
 

Reply to 2 switched lives for extractor? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I've installed a replacement bathroom extractor fan. Pic on the left is the old one. Pic on right is the new one. Wired the same way but the fan...
Replies
4
Views
879
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
1K
Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
363
1964 house old style wiring Need to wire a extractor fan up Is it possible to wire the extractor fan to report switch there's 2 red wires in the...
Replies
14
Views
928
Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
753

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock