Discuss 2 way switching pir led in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
22
Been to fit new led pir flood. 3core +e. Perm live. Sw live. N e.
Flood is 2core. So wired it perm live set up works a treat. Customer rings up wants it on switch. After investigating switch is a 2 way.. any way of doing this so works on pir then on with switch.
It's a sealed led light 2 core.
 
Some if these lights have a latch circuit, you have to turn the supply off and then on again quickly and it latches on until you turn it off then on again slowly, then it reverts back to PIR mode. Maybe worth checking instructions!
 
If you have only a line and neutral connection to an integrated sealed LED PIR light then you cannot have a manual ON switch as the wiring cannot bypass the PIR.
You can have a manual OFF switch, as you just switch the line to the light.

If you were to open up the LED light then you might be able to rearrange the wiring so that you have a connection direct to the LED and then with only a two way switch you would have to have it that the PIR sensor was disconnected whilst it was in manual ON, which would mean restarting the sensor once the switch was operated. This often causes the PIR to come on for a while!
 
Last edited:
If you have only a line an neutral connection to an integrated sealed LED PIR light then you cannot have a manual ON switch as the wiring cannot bypass the PIR.
You can have a manual OFF switch as you just switch the line to the light.

If you were to open up the LED light then you light be able to rearrange the wiring so that you have a connection direct to the LED and then with only a two way switch you would have to have it that the PIR sensor was disconnected whilst it was in manual on, which would mean restarting the sensor once the switch was operated. This often causes the PIR to come on for a while!
That was my thinking but don't want to open light up. Must have been a old halogen light that was fitted with perm live and sw live terminal or cut into pir / lamp circuit
 
Would my suggestion not work? So when the switch is on it feeds what would be the switched live of the PIR therefore powering the fitting? When the switch is off the PIR would work as normal?
If there were access to the switched line on the light fitting then it would work though with a 2 way switch the power to the PIR sensor would be switched off when the light is on manual.
PIR light with 2 way switch.jpg
However in this case there is no access to switched line to the light only permanent line to the PIR sensor.
 

Reply to 2 way switching pir led in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
827
Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
Replies
1
Views
436
Is the following set up possible with a 3 Gang 2 Way Smart Wifi Switch set up (the black glass type touch ones) One of the 3 switches, switches...
Replies
2
Views
510
Hi all, I just found this forum last night and figured I would post my issue since I can't find much out there with a similar situation. My job...
Replies
4
Views
403
Hi all, Just a quick one, I want to use an ip rated light switch with a neon indicator to manually ovveride a PIR detector controlling an e27 LED...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock