Discuss 208V Single phase wiring from 3 phase 4 wire disconnect in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I work in a location that was once a Machine shop showroom. We have 208/230/480 etc in the building. I need to install a temperature chamber that requires single phase only 208V or 230V supply. I have a 100 amp rated disconnect literally in the exact location this needs to go. I've read for hours and while I understand the basics of phased electricity supplies, I don't find anything definitive that gives me enough confidence to connect our new $24K instrument to this disconnect. The 3 phase system here uses red/blue/black color coding and does have a 4th wire neutral or ground. Can I safely run a single phase device from 2 phases of the disconnect? Are A and C the ones to use or does it matter? What do I do with the 3rd wire from the chamber? Is it tied to that neutral/ground also?

I know this topic gets beat to death, but looking for some reassurance on how to proceed? We're an electronic repair company and while we have lots of specialized knowledge in DC and RF, it doesn't translate all that well to phased electricity theory.

Thanks in advance!
Steve
 
What does the chamber need? Spec, etc?

Some only need a 208-230V supply, others might expect/need a mid-point connection as your 110V-0-110V style of high power domestic supply has.
[automerge]1587148122[/automerge]
Also to add if you do go to check voltages make very sure that your test meter is rated to at least 600V CAT-III if you are looking at a 3-phase board.
Some of the better electronics style multimeters are (e.g Fluke 179) and you can get suitable meters for under £100 in the UK. It is important as a mistake with an underated meter can end very badly. And I mean very badly.
[automerge]1587148532[/automerge]
Actually I should have been more specific, you must make sure that both the meter and the probes are suitably rated.
 
Last edited:
I work in a location that was once a Machine shop showroom. We have 208/230/480 etc in the building. I need to install a temperature chamber that requires single phase only 208V or 230V supply. I have a 100 amp rated disconnect literally in the exact location this needs to go. I've read for hours and while I understand the basics of phased electricity supplies, I don't find anything definitive that gives me enough confidence to connect our new $24K instrument to this disconnect. The 3 phase system here uses red/blue/black color coding and does have a 4th wire neutral or ground. Can I safely run a single phase device from 2 phases of the disconnect? Are A and C the ones to use or does it matter? What do I do with the 3rd wire from the chamber? Is it tied to that neutral/ground also?

I know this topic gets beat to death, but looking for some reassurance on how to proceed? We're an electronic repair company and while we have lots of specialized knowledge in DC and RF, it doesn't translate all that well to phased electricity theory.

Thanks in advance!
Steve
Steve welcome to the forum and yes you can put a double pole breaker in that panel. What amperage and voltage do you actually need
[automerge]1587210699[/automerge]
Steve welcome to the forum and yes you can put a double pole breaker in that panel. What amperage and voltage do you actually need
We know the voltage but what is the amperage and is the disconnect fusible or non fusible
 
Hi all and thanks for the replies. The disconnect is 100 Amp fused with large fuses and tabs on the end, RK5 maybe. All the info I have right now is single phase optional 208V or 230V, 30A.
You will have to lower the fuses depending on what amperage you need and just use A and C phase and does that disconnect have a neutral or does the machine need a neutral
 
You will have to lower the fuses depending on what amperage you need and just use A and C phase and does that disconnect have a neutral or does the machine need a neutral

Thank you or the reply. I was planning to change fuses to 30A per specs and the disconnect does have a neutral so it will be there if needed. Phase A and C are effectively single phase though, correct? Not "truly single" as I understand it, but still usable as single phase.
 
Thank you or the reply. I was planning to change fuses to 30A per specs and the disconnect does have a neutral so it will be there if needed. Phase A and C are effectively single phase though, correct? Not "truly single" as I understand it, but still usable as single phase.
Steve yes it would be a 30 single phase application, just remove the B phase fuse
 

Reply to 208V Single phase wiring from 3 phase 4 wire disconnect in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, searched the forum but cant locate anything similar so apologies if ive missed something. Ive got a new hob to install in the kitchen...
Replies
5
Views
1K
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
698
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
276

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock