hightower
One of my faults was that there was a break in one of the lines on the 3-phase motor circuit. I started doing a bit further testing as wasn't sure if that was enough, and found out L1 and N had been reversed.
Assessor came over, "have you found the faults?" I said "yeah, I found a break on L1 and investigating further told me L1 had been reversed with N". He said "what? No, it's just a break in L1". I told him what I'd found and it took him back a bit I think that I'd gone that bit further, like he wasn't expecting it. "Nah, just put down break in L1, forget about what the other bit"
Assessor came over, "have you found the faults?" I said "yeah, I found a break on L1 and investigating further told me L1 had been reversed with N". He said "what? No, it's just a break in L1". I told him what I'd found and it took him back a bit I think that I'd gone that bit further, like he wasn't expecting it. "Nah, just put down break in L1, forget about what the other bit"