- Reaction score
- 25,517
Is it earthed by way of the cable sheath if so can you direct Ze to the sheath.
Discuss 25 ohms Zdb + same reading for all circuits in the UK Electrical Forum area at ElectriciansForums.net
They could do "Zs" with N & E probes both to the N and should get the same for PFC and PSCC and it should be in keeping with the supply rating.I had some silly Zs readings once and I just hadn't zeroed the meter properly. Were the R1+R2 readings done with the same probes?
Agreed, but high Zs means either nothing useful in terms of parallel paths to the true Earth vis service pipes, etc. Or the meter (or its probes) is borked!When you took Ze did you disconnect the main earth lead away from the installation. We dont want parallel paths.
Reply to 25 ohms Zdb + same reading for all circuits in the UK Electrical Forum area at ElectriciansForums.net