Discuss Loop Impedance reading in the UK Electrical Forum area at ElectriciansForums.net

EddieB

-
Arms
Reaction score
27
Hi
I bought a holiday lodge last month and decided to test the circuits to see how they measured. The lodge itself is fed from a central point in the holiday village by a 16mm PVCSWA. The main earth wire terminates into a MET it looks to be a 10mm earth that is crimped onto the incoming earth, I cannot see what its crimped onto as the head the mains terminated into prevents this. Anyway I carried out the the normal tests on the circuits R1 R2 RN and these tested all within the expected parameters as an example the one of the rings measured R1.24 RN.24 R2 .39 and R1/R2 .25.
The other circuits all tested within expected parameters. The Ze measured .6, however when I powered up and did a Earth Fault loop impedance test the machine measured 23 ohms, this was repeated on all the sockets and the same measurement. Assistance required please as to the possible reason (s) for this.
 
Something not right

I would probably try checking the loop impedance at the outgoing side of the mcbs and try to narrow it down and recheck the resistance readings etc
 
you could have errors caused by RCD or MCB. worst i ever saw was a Ze of 0.2 but measured on the outgoing terminals of the rCD it was 341.
 
Something not right

I would probably try checking the loop impedance at the outgoing side of the mcbs and try to narrow it down and recheck the resistance readings etc
Thanks for the response.
Yep I agree something is not right, when you say check the loop impedance at the outgoing side of the mcb what do you actually mean, I checked both ring circuits and cooker circuit and they read 23 ohms,
I haven't yet checked lighting circuits, but if 3 circuits read around the same then where now?
 
Thanks for the response.
Yep I agree something is not right, when you say check the loop impedance at the outgoing side of the mcb what do you actually mean, I checked both ring circuits and cooker circuit and they read 23 ohms,
I haven't yet checked lighting circuits, but if 3 circuits read around the same then where now?
Could be the DB

You can check in a few spots, external, also where your socket wires connect into dB and along the final circuit
 
Ya your Ze and R1 and R2 are normal so

I'd be sticking a probe on the earth bar and checking fault loop at main switch ,rcds, mcbs on the outgoing sides

Did you disconnect anything at the met

May not turn out to be that at all either
I’ll go through it as you describe and I’ll let you know, as an aside I disconnected the main earth for the Ze test but reconnected it after. ?
 
I would put my bets on RCD uplift as @telectrix suggested, I had some BG ones a while ago that made some circuits wildly high Zs.
If you can do a bypassed Zs on the circuit that will prove it one way or another. To do this I isolate the supply then put a R1+R2 link cable in between live and earth at the furthest point on the circuit in question. Then put the tester on high loop and place between the outgoing circuit feed and the non isolated incoming live, this will give you a non uplifted reading to compare with your current one!
Be very careful when doing this test!
 
Last edited:
I would put my bets on RCD uplift as @telectrix suggested, I had some BG ones a while ago that made some circuits wildly high Zs.
If you can do a bypassed Zs on the circuit that will prove it one way or another. To do this I isolate the supply then put a R1+R2 link cable in between live and earth at the furthest point on the circuit in question. Then put the tester on high loop and place between the outgoing circuit feed and the non isolated incoming live, this will give you a non uplifted reading to compare with your current one!
Be very careful when doing this test!
Thank you for replying, funny enough these are BG RCD's, If it is the RCD I can bypass it by feeding a spare MCB from the incoming feed block the neutrals from the mains
and then test the ring.
I would appreciate a sketch showing the process you describe , you can either email it to me or put it on here whatever is the easiest if you wouldn't mind.
you could have errors caused by RCD or MCB. worst i ever saw was a Ze of 0.2 but measured on the outgoing terminals of the rCD it was 341.
Telectrix, thanks for reply, I appreciate it.
 
here is a method.you turn off the RCD and/or MCB. short L-E at point you want to measure. them MFT on hi current Zs setting (2 leads).bridge to RCD.MCB with the meter. this will give you a true Zs.
High current Zs test with RCD.jpg

don't forget to remove the short before re-energising.
 
here is a method.you turn off the RCD and/or MCB. short L-E at point you want to measure. them MFT on hi current Zs setting (2 leads).bridge to RCD.MCB with the meter. this will give you a true Zs.
View attachment 90663
don't forget to remove the short before re-energising.
Good method, can't say I've ever had to carry this type of check in practice,don't even have a 2-wire tester

The theory is routine enough though
 
Is the high current reading like 20a ?

Better for troubleshooting those issues
something like that. the higher current helps to get past tarnished contacts, that's why low current test often gives slightly different results. ( well that's my theory, anyway ).
 
something like that. the higher current helps to get past tarnished contacts, that's why low current test often gives slightly different results. ( well that's my theory, anyway ).
Yes that's my theory on the low current testing , should be more reliable at the higher current here

Similar to IR troubleshooting at 1000v where it can be more effective at locating a fault, when safe to test
 
I would put my bets on RCD uplift as @telectrix suggested, I had some BG ones a while ago that made some circuits wildly high Zs.
If you can do a bypassed Zs on the circuit that will prove it one way or another. To do this I isolate the supply then put a R1+R2 link cable in between live and earth at the furthest point on the circuit in question. Then put the tester on high loop and place between the outgoing circuit feed and the non isolated incoming live, this will give you a non uplifted reading to compare with your current one!
Be very careful when doing this test!
Dont think you'll find these particular tests in any reference books will you ?
 

Reply to Loop Impedance reading in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
723
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
527
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
884
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock