Posting a message to the forum will remove the above advertisement

Discuss 3 phase distribution in the Industrial Electrician Talk area at ElectrciansForums.co.uk.

Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. Tom Ashcroft
    Offline

    Tom Ashcroft New EF Member

    Hi all,
    Just an enquiry..
    Our company have recently moved factory's. I am talking a very small unit.
    At the moment there is one TPN distribution board which is at the top end of the factory..
    Is there any problem running a 3 phase supply off a 63amp mcb which will feed the new d/b just to keep run of cables down to small sockets and lighting power.
     
  2. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    There will be a lack of discrimination having MCB's in series. A switch fuse/fused switch to feed new distribution circuit would be a better design IMO.
     
  3. Tom Ashcroft
    Offline

    Tom Ashcroft New EF Member

    I would still have to feed the fused switch off the existing d/b though off a 63amp MCB.
     
  4. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    That would be pointless though as your left with the same situation you were trying to eliminate by using a switch fuse. Why would you have to feed it from an MCB? What make is the existing DB?
     
  5. Tom Ashcroft
    Offline

    Tom Ashcroft New EF Member

    The existing d/b is a Schneider ISO acti 9
     
  6. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    • Like Like x 2
  7. westward10
    Offline

    westward10 Ugly kids what a disappointment. Electrician's Arms

    Location:
    Northamptonshire
    I see the discrimination point but in this situation I probably wouldn't consider it too much.
     
  8. i=p/u
    Offline

    i=p/u Trusted Advisor

    Either or providing you've got lights to see what u doing
     
  9. darkwood
    Offline

    darkwood For it is a human number, its number is 666 Staff Member Electrician's Arms

    Location:
    West Yorkshire
    Depends here on your supply incoming, if you only have a 3ph 100amp supply then discrimination is impossible and at best only partial which really means nothing, if the company would see great losses at a power failure due to lack of dscrimination if the wrong device tripped then it's a problem, if this is just an inconvenience then as long as it is made clear to the customer it is really not an issue, if it is then you need to split the supply if the option exists and fit a larger cable and have fully discriminated front end fusing, as long as the customer is made aware of all the options and get it in writing or email then your ass is covered.
     
  10. westward10
    Offline

    westward10 Ugly kids what a disappointment. Electrician's Arms

    Location:
    Northamptonshire
    Think this is being over whipped, most of us ignore discrimination everyday by having 13A fuses in our plug tops and FCUs.
     
  11. darkwood
    Offline

    darkwood For it is a human number, its number is 666 Staff Member Electrician's Arms

    Location:
    West Yorkshire
    On a factory level install, discrimination is important as it can be costly to get it wrong especially if production time is lost through bad discrimination, agree about domestic as the incoming is too small to achieve full discrimination and any circuit really so more often than not it not even factored in, these 5week short courses probably don't even bother teaching it although I stand corrected on that point.
     
    • Like Like x 1
  12. westward10
    Offline

    westward10 Ugly kids what a disappointment. Electrician's Arms

    Location:
    Northamptonshire
    I wonder what sort of "factory" it is with one TP board at the main intake.
     
  13. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    Fuses compliant to BS EN / IEC 60269-1 or 60269-2-1 will provide total short circuit selectivity/discrimination when the rated current of the upstream fuse is 1.6 times the rated current of the downstream fuse. If the main fuse was 100A then ideally the fuse downstream ( in the switch fuse) would be rated at no more than 63A if full selectivity was/wanted to be achieved.
     
  14. darkwood
    Offline

    darkwood For it is a human number, its number is 666 Staff Member Electrician's Arms

    Location:
    West Yorkshire
    That's fine Lee until you start mixing ocpd types ..ie you need a 160amp mccb to give full discrimination on an mcb board and if I recall a 63amp mcb give full discrimination again similar mcbs only up to 10amp ....not sure of the standards you hi-light there but are you sure it's against short circuit with full discrimination when you cite those standards, sounds like overload discrimination to me.
     
  15. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    Yeah I agree that things become a little more tricky when mixing OCPD types.

    60269-1 is the international standard for Low-voltage fuses - General requirements and 60269-2 is the international standard for Low-voltage fuses - Supplementary requirements for fuses for use by unskilled persons.

    View attachment 35139

    The OP says the new board is for small power and lighting. Looking through various charts and comparing the total operating I2t of a 32A B type MCB and pre-arching I2t of the 63A fuse he should be good up to a maximum fault current value for which full discrimination is ensured of around 2.4KA. If the Zdb at the new board was lower than 0.10 ohms he might have a problem.
     
    Last edited: Jan 7, 2017
Loading...
Similar Threads - phase distribution Forum Date
Single phase distribution for small flats Electrical Forum Oct 11, 2016
Three phase TT install with distribution circuit and RCBOs Electrical Forum Oct 10, 2016
RCD protection on 3 phase sockets/18th edition Electrical Forum Tuesday at 11:19 PM
crabtree c50 3 phase mcb Electrical Forum Jul 11, 2017
Phase 3 is importing! Phase 1&2 are exporting as usual. Hyrdoelectric Power Forum Jun 29, 2017
How to determine the Line and Phase current and power of a three phase installation? Electrical Wiring, Theories and Regulations Jun 8, 2017

Share This Page

  • Electricians Directory Post a Domestic Job Post a Commercial Job