Discuss 3 phase distribution in the Industrial Electricians' Talk area at ElectriciansForums.net

T

Tom Ashcroft

Hi all,
Just an enquiry..
Our company have recently moved factory's. I am talking a very small unit.
At the moment there is one TPN distribution board which is at the top end of the factory..
Is there any problem running a 3 phase supply off a 63amp mcb which will feed the new d/b just to keep run of cables down to small sockets and lighting power.
 
I see the discrimination point but in this situation I probably wouldn't consider it too much.
 
Depends here on your supply incoming, if you only have a 3ph 100amp supply then discrimination is impossible and at best only partial which really means nothing, if the company would see great losses at a power failure due to lack of dscrimination if the wrong device tripped then it's a problem, if this is just an inconvenience then as long as it is made clear to the customer it is really not an issue, if it is then you need to split the supply if the option exists and fit a larger cable and have fully discriminated front end fusing, as long as the customer is made aware of all the options and get it in writing or email then your --- is covered.
 
Think this is being over whipped, most of us ignore discrimination everyday by having 13A fuses in our plug tops and FCUs.
 
On a factory level install, discrimination is important as it can be costly to get it wrong especially if production time is lost through bad discrimination, agree about domestic as the incoming is too small to achieve full discrimination and any circuit really so more often than not it not even factored in, these 5week short courses probably don't even bother teaching it although I stand corrected on that point.
 
Fuses compliant to BS EN / IEC 60269-1 or 60269-2-1 will provide total short circuit selectivity/discrimination when the rated current of the upstream fuse is 1.6 times the rated current of the downstream fuse. If the main fuse was 100A then ideally the fuse downstream ( in the switch fuse) would be rated at no more than 63A if full selectivity was/wanted to be achieved.
 
That's fine Lee until you start mixing ocpd types ..ie you need a 160amp mccb to give full discrimination on an mcb board and if I recall a 63amp mcb give full discrimination again similar mcbs only up to 10amp ....not sure of the standards you hi-light there but are you sure it's against short circuit with full discrimination when you cite those standards, sounds like overload discrimination to me.
 
That's fine Lee until you start mixing ocpd types ..ie you need a 160amp mccb to give full discrimination on an mcb board and if I recall a 63amp mcb

Yeah I agree that things become a little more tricky when mixing OCPD types.

60269-1 is the international standard for Low-voltage fuses - General requirements and 60269-2 is the international standard for Low-voltage fuses - Supplementary requirements for fuses for use by unskilled persons.

View attachment 35139

The OP says the new board is for small power and lighting. Looking through various charts and comparing the total operating I2t of a 32A B type MCB and pre-arching I2t of the 63A fuse he should be good up to a maximum fault current value for which full discrimination is ensured of around 2.4KA. If the Zdb at the new board was lower than 0.10 ohms he might have a problem.
 
Last edited:
They are for bs88 fuses hence my original query these standards don't apply to mcb's and rcd's which is what we use commonly... ill try find the discriminating charts for mcbs.
 
They are for bs88 fuses hence my original query these standards don't apply to mcb's and rcd's which is what we use commonly... ill try find the discriminating charts for mcbs.

Yeah but the fuses in the head will more than likely be 1361's now BS88 and the fuse in the switch fuse will be BS88 which will provide discrimination if 100A up stream and 63A down stream. A 32A b type 60898/61009 will partially discriminate with the 63A BS88 but full discrimination can be achieved if Zs/Zdb isn't any lower than .10 ohms.
 

Reply to 3 phase distribution in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
282
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
591
When there exists a single-phase transfer switch within a 3-phase distribution system, is it necessary for both feeds to the transfer switch to be...
Replies
8
Views
753
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
654

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock