Hi folks,

I'm project managing a 30kW PV installation on a social club and could use a bit of advice -

Main board is an old Ottermill F frame (the board has no plates; I had to track down an ex Ottermill employee who ID'd it from photo's).

We'll be installing a new TP&N 3 phase sub-board exclusively for the PV, in the same plant room and within 3 metres of the main board - I'm getting conflicting advice re the connection of the new sub-board to the existing DB1.


  • One contractor is advising that it can be connected directly to the main incommer in DB1 because the sub-board is within 3m of it.
  • Another contractor is saying the cable must be protected by an MCCB in DB1.

The issue is that the MCCB for this old board (Westinghouse Series C FDB3060L) is a legacy item and eye-wateringly expensive as a new piece. I can buy a used one off e-bay for reasonable money but I'm reluctant to fit 2nd hand gear.

If the conductor can be fitted direct to DB1 without the 60A MCCB it would solve problems - my question: would this be compliant?

Many thanks
 
Hi folks,

I'm project managing a 30kW PV installation on a social club and could use a bit of advice -

Main board is an old Ottermill F frame (the board has no plates; I had to track down an ex Ottermill employee who ID'd it from photo's).

We'll be installing a new TP&N 3 phase sub-board exclusively for the PV, in the same plant room and within 3 metres of the main board - I'm getting conflicting advice re the connection of the new sub-board to the existing DB1.


  • One contractor is advising that it can be connected directly to the main incommer in DB1 because the sub-board is within 3m of it.
  • Another contractor is saying the cable must be protected by an MCCB in DB1.

The issue is that the MCCB for this old board (Westinghouse Series C FDB3060L) is a legacy item and eye-wateringly expensive as a new piece. I can buy a used one off e-bay for reasonable money but I'm reluctant to fit 2nd hand gear.

If the conductor can be fitted direct to DB1 without the 60A MCCB it would solve problems - my question: would this be compliant?

Many thanks

If the swa is big enough to be covered by incomer fuse then no problem with either option
 
Thanks Shanky,

There's a 50A 3 pole MCB in the new sub and 3 x 20A 500V fuses in the Otermill DB1 - do you mean the swa between the 2 boards?
 
Why is the cost of the circuit protection an issue at install?
This should have been considered at the assessment stage if the design was being undertaken by a competent person, so fit the correct kit, and do the job right, if the job has not been surveyed and designed correctly then sort out the surveyor and designer so they are looking for new jobs, because they are obviously incompetent.
 
#4 -Thanks for the input NetBlindPaul - the surveyors assessment at pricing stage was that the sub-board circuit would be connected directly, without an MCCB being required, so it wasn't costed for.

Now, months down the track, I'm politically locked into a contractor (connected with the facility) who says the opposite.

From a technical point of view, what's your opinion on the 2 solutions - are they both valid or is one or both not compliant?
 
#4 -Thanks for the input NetBlindPaul - the surveyors assessment at pricing stage was that the sub-board circuit would be connected directly, without an MCCB being required, so it wasn't costed for.

Now, months down the track, I'm politically locked into a contractor (connected with the facility) who says the opposite.

From a technical point of view, what's your opinion on the 2 solutions - are they both valid or is one or both not compliant?

I can't say from where I am, I have not got enough information on the detail of the install apart from one piece, the surveyor/designer is incompetent.
So get them to sign for the design, job done.
 
Time to dig deep or go 2[SUP]nd[/SUP] user. There is a company that specialises in Ottermill gear in Totnes I think. It’s run by ex Ottermill staff so they should know what they’re on with.
A few years back they supplied me with fixed isolation contacts for an ACB, I didn’t think they were too bad on price.
I’ve never dealt with any of Ottermill’s small stuff though.

I certainly wouldn’t connect in to the incoming.
 
Nice one!

As I say it’s a long time since I had anything to do with Ottermill.

We had the isolating contacts overheating on the transformer incomer. No idea where to get spares so it was a case of plunder another board to get us up and running.
One thing I do remember, they were absolute pigs to get to. Set off attacking from the front, gave up there and set to digging my way in from the back.
Change three contacts? It must have taken me five hours!

Ottermill ACB’s were good, the fuse switches absolute crap.
 

Reply to 3 phase Sub-board, supply conductor protection in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
Hi Looking at a job currently adding a 3 phase solar installation but the distribution board is full obviously a new board is the best option but...
Replies
9
Views
1K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
What are people fitting in the 3 phase range just lately, I've had a scan at various makes and it seems to be a ---- up between Hager and Wylex at...
Replies
9
Views
851

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock