Your line to line voltage indicates you may have a split phase supply and the fact there is 0v between L1 and L2 points to them being on the same phase.
 
I was called out a few years ago to a faulty compressor..
Spoke to the sparky on site who confirmed all was ok, voltages checked, fuses ok, etc..
One of the fuses to the compressor had blown, L1 going through winding and back up onto L2 fuse..
said he had checked both sides of fuses and they were all live, he scratched his head for a while, drew him the circuit and the penny dropped...
I put it down to a faulty overload, saved him his blushes
 
At what position in the installation are you doing your tests?
It needs to be right at the incomer on the supply side with the load side isolated
 
Have you asked the experienced guys what they think, have they done or supervised any of this testing?

You should apply for the trainee part of the forum if you are an apprentice, that way answers are tailored better suited for someone who is learning. Will also get less grief for asking what would be a silly question for someone experienced.
 
You should apply for the trainee part of the forum if you are an apprentice, that way answers are tailored better suited for someone who is learning. Will also get less grief for asking what would be a silly question for someone experienced.[/QUOTE]
Well there on the same site but doing other bits so thought I’d ask so I kind of know what I’m talking about
 
Only 2nd year and I know just like to show I kind of know what I’m looking for and at
L1-L2 Nothing
L2-L3 450v
L1-L3 450v
L1-N 230v
L2-N 230v
L3-N 230v

So if I connect all sub circuits the same then there should be no issues?
 
Bradly
There are two main possibilitys, If it is rural and fed off its own pole mounted transformer it could be a split phase supply where the transformer is HV to 500V with a center tap giving 250V between each end to the center neutral tap and 500V between the outers.
If it is in a town it may be fed off an old DC cable which has been converted to two phase and neutral.
A third option is that it is a cable fault with an open circuit/weld.
 
The voltage measured between the lines (450V) suggests a split-phase 230-0-230 supply rather than two phases out of a 3-phase 400/230V system.

A look at the meter(s) will confirm as they will have the appropriate spec for the supply in use. Also, if the HV feeding the transformer is single-phase (with two lines only) then the LV service must be split-phase.

If you are only connecting single-phase loads, then you can follow normal practice. If this is the main DB with one outer shared between the L1 & L2 ways, the total load load on those should probably equal the load on the L3 ways.
 
The voltage measured between the lines (450V) suggests a split-phase 230-0-230 supply rather than two phases out of a 3-phase 400/230V system.

A look at the meter(s) will confirm as they will have the appropriate spec for the supply in use. Also, if the HV feeding the transformer is single-phase (with two lines only) then the LV service must be split-phase.

If you are only connecting single-phase loads, then you can follow normal practice. If this is the main DB with one outer shared between the L1 & L2 ways, the total load load on those should probably equal the load on the L3 ways.
Hi thanks, I have some double pole switches and single pole so just connect as normal?

I also have a 3 phase pool to wire up so I’m not sure how that’s going to work yet
 
Hi I have double pole switches eg 2 lives from there and then just single pole MCBS

Have pool to do which is 3 phase but I’m not sure what needs to be done with thay
Make sure you get the phase sequence the right way around Mate otherwise when you empty the pool the dain water will go in a different way than normal:tongue::mouth:.
 
I also have a 3 phase pool to wire up so I’m not sure how that’s going to work yet
The pool will work fine, the pumps however are a different story.

You need to confirm if you have two or three phases otherwise it’s going to start getting expensive.
 
The pool will work fine, the pumps however are a different story.

You need to confirm if you have two or three phases otherwise it’s going to start getting expensive.
Well I have split phase supply all my outgoing circuits are either single pole or the use of 2 phases eg black and brown from a 2 pole MCB so there all fine just the one pool
 
Well I have split phase supply all my outgoing circuits are either single pole or the use of 2 phases eg black and brown from a 2 pole MCB so there all fine just the one pool
It sounds very much like you don't have a three phase supply so connecting three phase equipment is not advisable as it will not work correctly and worst case it could be damaged which will get expensive.
 

Reply to 3 phase test readings help in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Probably more of a maths problem than anything else / managing to confuse myself. I have been asked to look at energy consumption of some...
Replies
7
Views
559
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
465
Hi, searched the forum but cant locate anything similar so apologies if ive missed something. Ive got a new hob to install in the kitchen...
Replies
5
Views
1K
Hello, I’m testing some electric meters. As the circuits have no load on them to prove each ct I’ve plugged a hair dryer to simulate a load and...
Replies
3
Views
473
Been called to help a friend who can't get anyone to look at his car lift until next week and it's stopping him from working. I said I'd have a...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock