Hello,

I’m testing some electric meters.
As the circuits have no load on them to prove each ct I’ve plugged a hair dryer to simulate a load and put the ct around the line of the hair dryer to check measurements are the same as a calibrated meter.
The Ct’s from each phase read the same Amps however the kw reading is twice as high for the L2 Ct which is the circuit the socket is plugged into.
This also occurred when the sockets where L3 circuits in a different location then the L3 ct had twice the kw but the same amps as the other phases.
This was the same every time.

Would anyone know why this occurs ?
Many thanks
 
I think a diagram could help, also i assume your KW readings are from the meter you are testing. Again assume your hairdryer is single phase and the meters are three phase. How the meters are connected ? Type of meter?
End of the day to get accurate KW you need an accurate current and an accurate voltage.
 
I think a diagram could help, also i assume your KW readings are from the meter you are testing. Again assume your hairdryer is single phase and the meters are three phase. How the meters are connected ? Type of meter?
End of the day to get accurate KW you need an accurate current and an accurate voltage.
hi,
Yes your right single phase dryer, Carlo gavazzi 271 meters and yes the reading is from the meter.
 
Have fitted those before. Not wanting to state the obvious but it is vital that the voltage inputs to the meter, L1, L2, L3 match exactly with the L1, 2, 3 current transformers. i.e. the line that you designate as L1 for voltage has to be the same line you designate for L1 for the CT
Please see connection diagrams in https://www.gavazzi.no/wp-content/uploads/EM271DS.pdf
Dont forget the neutral connection to the meter , also
 

Reply to Different kw readings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All done an EICR on a small office around 5 years old someone has added extra socket circuits from new to suit layout. they have added...
Replies
6
Views
1K
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
842
G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Replies
5
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock