Discuss 3 phase USA 3/60/220 to UK 3 phase is it doable thanks in the UK Electrical Forum area at ElectriciansForums.net

You want to run a 220v device on 400v?

a transformer may be suitable but motor will run slightly slower due to the reduced frequency.

what is the device to be powered?
 
A transformer can be used to correct the voltage, but the difference in frequency might be a problem. All AC motors that don't have variable-speed drives will run too slowly and might not work correctly. You would need to seek advice from the manufacturers as to whether it is capable of operating at 50Hz. If not, a frequency converter will be needed which is significantly more complex and expensive than a transformer, or some motors might need changing, or whatever. One would need very specific information about them to decide which methods would be best.
 
A transformer can be used to correct the voltage, but the difference in frequency might be a problem. All AC motors that don't have variable-speed drives will run too slowly and might not work correctly. You would need to seek advice from the manufacturers as to whether it is capable of operating at 50Hz. If not, a frequency converter will be needed which is significantly more complex and expensive than a transformer, or some motors might need changing, or whatever. One would need very specific information about them to decide which methods would be best.
 
I've a few machines running on 220v three phase.

The motors on my machines are servo, so are controlled by individual yaskawa drives.

I am using a 400v - 220v transformer.

It might be worth finding out if the machine has PNP or NPN components.

You might find it difficult keeping a ready supply of NPN spares.
 

Reply to 3 phase USA 3/60/220 to UK 3 phase is it doable thanks in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
732
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
344
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
958
Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
1K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
301

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock