Discuss 3 storey,9 bed HMO just needs a few lithium smoke? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi, I'm completely rewiring a 9 bed 3 storey HMO in Jan, The fire detection required is just some linked lithium detectors in the bedrooms/hallways kitchen etc with some emergency lights in the hallways. The thing is I'm doing the rip out after Christmas and I'll be removing everything including a fire alarm panel, break glasses ,FP200 etc , emergency bulkheads and exit signs. This is what was required when it was just a 7 bed 2 storey HMO ( attic conversion is happening). I'm not designing the system, obviously, just installing it to the specs given. The question really is , does this sound right?. I've done loads of smaller HMO's with break glass systems and recently 2 sprinkler systems in relatively small houses ( non hmo) so I just find it hard to believe the landlord has got off so lightly. Any input is welcome.
 
What Category of system does the design denote?
I would be seeking professional advice and a risk assessment, what they are proposing sounds wholly inadequate.
 
D1: LD2 Bs5839 part 6 2019, that was what was quoted to me by the fire assessor when I asked them to double check the required system
From what I can see ( and I am no expert at all on fire design) grade A in communal areas and D LD3 in beds or grade A all the way through for a 3 storey hmo. but i have been wrong many times before.
answering my own questions now. this city of bristol document makes fire panels redundant almost, grade D1 for everything it seems, which is why the council agreed with the fire guy
 
Last edited:
It doesn’t sound right to me, as you are installing it I would get a second opinion. I know the a house of single ocupancy over 250m sq. over three floors requires more than linked optical smokes etc.
 
No-one I know thinks it sounds right but the designer says it's fine , the council says it's fine, I did email my NIC assessor/engineer for his opinion, obviously no reply there. In the end I will not be signing off on the design just the install and commissioning . also i guess this means no Db check in each room or yearly smoke test or emergency light test .Maybe we'll just have to wait until the whole thing is finished then put some nice trunking everywhere for an' actually you do need a proper panel' moment.
 
No expert, but a quick google and a document from an HMO architect website states Grade A in communal areas and Grade LD2 or LD3 in the individual rooms for 3 storey buildings.

Emergency lighting is a must.
 
My understanding is since the 2005 fire regulatory reform act, a fire risk assessment should be provided for a dwelling to operate as a HMO.
The risk assessment will in turn stipulate the safety measures required.
Building regs sometimes don't follow this up assuming the HMO registration process will catch it. It can fall between the cracks.

If it were me I'd be asking to see the risk assessment in order to make sure what I fit complies with it.
 
I've looked at the fire assessment from the last HMO I did for the same landlord and fire assessor, the risk assessment is pretty worthless, it's a templated list of potential issues and then whether or not they apply to the building and if they do what are you going to do about it .If fire is a risk and the solution is a set of lithium smokes then that's what they will put on the risk assessment and in the plans, it's really whether or not the risk assessor who is also the fire design guy wants to install a panel, which in this case he doesn't because he doesn't think he needs to.
It seems we all think he should have a panel but the risk assessment ,fire guy and council say he doesn't so I'll have to live with the fact that I think they are wrong but enough people have signed stuff to say it's right so I'll install it and invoice away.
Interestingly the risk assessment does say that a contractor will have to check the smokes on a yearly basis, can't remember being asked to do that on anything but a panel.
Thanks for your comments.
 

Reply to 3 storey,9 bed HMO just needs a few lithium smoke? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
307
I know this has been brought up before but as a QS for a housing association ,i have been asked my opinion on interpretation of the regulations...
Replies
11
Views
3K
Hi guys We have being asked to install some emergency lighting at a 3 storey HMO, the lighting has being designed and it’s basically being...
Replies
8
Views
4K
Having a bit of a mare at the moment with a small 2 story HMO (6 single rooms with shared kitchen) which was fitted relatively recently (2016 or...
Replies
18
Views
2K
hi guys Have a 3 storey house (loft converted) that is getting converted into a HMO with 5 x bedrooms, 1 x communal living room and 1 x communal...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock