Discuss 32 amp cooker switch on ring main? in the UK Electrical Forum area at ElectriciansForums.net

tomodo

-
Reaction score
7
Hi everyone, so ive got a new oven to install this one is rated at 16 amps, old one was 13 amps on a plug and socket to ring main. My question is can i install a 32amp double pole switch on the ring main then feed 4mm flex to the oven? Is there anything in the regs that prevents this? Thanks for reading.
 
Hi everyone, so ive got a new oven to install this one is rated at 16 amps, old one was 13 amps on a plug and socket to ring main. My question is can i install a 32amp double pole switch on the ring main then feed 4mm flex to the oven? Is there anything in the regs that prevents this? Thanks for reading.
it would be a 20A D/P switch. off the ring. however over 2.2kW ( 9A) appliances should be on a dedicated circuit. not potentially overloading the ring.
 
Agree with @telectrix about the 2.2kW. See below (iii) nicked from Appendix 15 of the regs.

1614879145704.png
 
Hi, My new cooker requires 32amp ELCB which is ready. What is the best and safest way to connect the cooker to its circuit? Cooker sales person told me to leave wire loose from wall and use a wire connector to connect it but my electrician thinks its safer to install the 15amp round pole plug and switch to connect them. My concern, can a 32amp cooker use a 15amp plug to connect to 15amp switch on a 32amp circuit? Would the 32amp cook3r overload the 15amp plug and switch?
 
Hi, My new cooker requires 32amp ELCB which is ready. What is the best and safest way to connect the cooker to its circuit? Cooker sales person told me to leave wire loose from wall and use a wire connector to connect it but my electrician thinks its safer to install the 15amp round pole plug and switch to connect them. My concern, can a 32amp cooker use a 15amp plug to connect to 15amp switch on a 32amp circuit? Would the 32amp cook3r overload the 15amp plug and switch?
If your cooker requires more than 15A then No!

You are down as Malaysia for country, I believe they typically use UK style 13A plugs and sockets now rather than the older 5A/15A round pin?

What make/model of cooker?

Generally most cooker circuits here in the UK are a dedicated radial circuit with 6mm cable and a 32A breaker. You get cooker switch/socket accessories designed for this where the cooker's cable can be terminated and joined via the switch to the supply cable. This sort of thing:

https://www.NoLinkingToThis/p/mk-lo...ker-switch-13a-dp-switched-socket-white/17157
 
If your cooker requires more than 15A then No!

You are down as Malaysia for country, I believe they typically use UK style 13A plugs and sockets now rather than the older 5A/15A round pin?

What make/model of cooker?

Generally most cooker circuits here in the UK are a dedicated radial circuit with 6mm cable and a 32A breaker. You get cooker switch/socket accessories designed for this where the cooker's cable can be terminated and joined via the switch to the supply cable. This sort of thing:

https://www.NoLinkingToThis/p/mk-lo...ker-switch-13a-dp-switched-socket-white/17157
My cooker is a Belling from UK. So in my case should I just follow the sales person advice to connect it to the circuit via wire connector?
 
@Jun Fang ,

Some of your posts are being moderated. When a post says something like "this is only visible to you", it's in the moderation queue waiting for staff to approve it. Please bear this in mind and wait for it to appear... posting the same thing multiple times won't speed up the process :)
 
My cooker is a Belling from UK. So in my case should I just follow the sales person advice to connect it to the circuit via wire connector?
Belling make a lot of different models, some have 13A plugs and others are intended for hard-wiring. The specifications for the specific model you are looking at is a good starting point!
 

Reply to 32 amp cooker switch on ring main? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
265
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
751
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
678
Hi all, I replaced my old Electrolux oven which operated with a 13 amp plug. The new Kenwood oven I ordered says a 16 amp (Requires hardwiring to...
Replies
13
Views
3K
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock