Discuss 32volts present at light fitting when it's switched off! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

T

Tim Brennan

i have a light fitting that 32volts across it when it is switched off. I have changed the switch, the rose, I've done insulation resistance on the cable to the switch, which is fine.
Not sure where the voltage is coming from and why only 32volts. I assuming that it must be cable insulation fault even though it metered at >299mohms.
I decided to run new cable in to that section of the circuit.
Any ideas?
 
Well if the light is still glowing when you've switched it off it's still got supply. Did this just start? Does it go off when you safe isolated that circuit at the CU?
 
I'm asking that because I've seen that before with a touch activated dimmer and an LED lamp. The touch dimmer requires a small current to operate the electronics, so it leaks through and there is enough juice to make an LED lamp glow.
 
No it's been a issue for a while, finally got round to sorting it out as part of a partial rewire, it does go off with safe isolation at the CU
 
Ok, I'd safely isolate, disconnect the switch cable and check IR on that cable with the switch off. Could be a high resistance fault on the switch cable itself. I'd rule that out first. Or have you replace the switch cable?
 
No it's been a issue for a while, finally got round to sorting it out as part of a partial rewire, it does go off with safe isolation at the CU
Ok, then my thought is the 30V is coming via the switch somehow (as per SC suggestion in #7) or you've got an additional connection to the lamp's switched live thats bypassing the switch. I've seen allsorts with home brewed two way switching and the next light in the circuit etc. If its simple enough perhaps try removing all other lamps on this circuit and see if the 30V disappears ?
 
Well, before I replaced the cables I did IR test on them, they all came up ok. Replaced them anyway. Now everything is back as it should be. But intriguing as to what was causing it, I inspected the insulation on the old cable, looked fine to me. Maybe I missed something.
 
Could be live & neutral cross connected between pendants loop in's/out's. When one light is turned on, presents voltage at dimmed light's neutral, if you get my drift. :)
 
To be honest, I never tried that, but I have found a number of scary things, the guy that was here before me must have been a diy enthusiast. I've found a single socket part screwed to a back box under the floorboards in one bedroom acting as a junction box! A borrowed neutral on the landing two way lights, and where they had moved the CU on the previous kitchen change, they had extended all the cables using chocblocks wrapped in tape, stuffed them into a hole in the wall, filled it with plaster and tiled over it. I found that little beauty when I took the tiles of to refit the kitchen, and noticed a line cable just showing where I pulled the tile off.
 
^^nothing surprises me when doing kitchen refits any more...... I won't give a firm price until the old units are out....

Earlier this week I was working on a bathroom refurb...

Taking a light off the wall - 2 cables - 1 x 2 core and 1 T&E.. the 2 core supplied the live off circuit 2, the T&E supplied the neutral from circuit 3, and neither run in a safe zone.

And the icing on the cake - neither circuit had an earth.... just shows the importance of safe isolation

Bathroom 1.jpg
 

Reply to 32volts present at light fitting when it's switched off! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all. Removed an ancient light fitting, replaced with a newer one, the light comes on but can't be turned off with the switch. It was working...
Replies
23
Views
772
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
Hi all, I'm in the UK and have recently had a ducted extractor fan Mixflo 200W with timer fitted. The fan comes on with the pull cord and runs for...
Replies
6
Views
296
Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
877
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
519

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock