Discuss 3phase breaker made of 3 single phase breakers in the UK Electrical Forum area at ElectriciansForums.net

Tim

-
Reaction score
66
Hi guys,

Is there a difference between 3 single phase breakers next to each other (with a linking bar) and 1 3 phase breaker?

Does the 3 phase breaker have anything special in it or is it just 3 single phase breakers stuck together with a bar in the switches?

Cheers,
Tim
 
On the side is a linking pin to the mechanical system of the ajoining breaker .... if it trips it then trips its adjoining mcb, its like a mousetrap - just needs a slight pressure to activate the trip.

The linking bar on the top where you operate them couldn't physically open the other breakers as it requires too much force ... the mcbs will all trip whether or not this switch bar was on or not.
 
Come on , fess up

what your really asking is can you retro bodge 3 single modules that you already have , into 1 3pole device cos the wholesalers are trying to spank you over the cost of a proper unit.

i can smell a scam a mile away lol.
 
On the side is a linking pin to the mechanical system of the ajoining breaker .... if it trips it then trips its adjoining mcb, its like a mousetrap - just needs a slight pressure to activate the trip.

The linking bar on the top where you operate them couldn't physically open the other breakers as it requires too much force ... the mcbs will all trip whether or not this switch bar was on or not.

Cheers for the quick reply.

I wasnt sure if the linking pin had another function. I was just going to pull one apart but i thought id ask here first.

Cheers,
Tim
 
Come on , fess up

what your really asking is can you retro bodge 3 single modules that you already have , into 1 3pole device cos the wholesalers are trying to spank you over the cost of a proper unit.

i can smell a scam a mile away lol.

Lol, it would make life easier if you could do that every time
 
And you could use 3 different amperage off breakers too.
One for a shower, one for a fan and one for a shaver unit. :eek:

Only playing, reference a recent thread.

Boydy
 
I agree with Biff, sounds like you're taking a chance but that's not a bad thing;). In this case it's not a good idea though, as Darkwood says it's not just the lever on the triple pole breaker that's physically joined, it's the internal tripping mechanisms as well so your idea won't work I'm afraid.
 
I had a similar thing on an EICR last year.
3 phase, the link between the breakers was broken, so 2 phases would go off, then you would have to flip off the other one separately.
I wasnt quite sure if I should give this a code.
I asked on the IET forum. The replies were "make an observation, not potentially dangerous".
Think of fuses supplying 3 phases - 3 separate fuses to take out, just like 3 separate CB's.

It isnt good practice to put a new install in with 3 separate CB's, but I cannot see it breaking any Regs.
 
And you could use 3 different amperage off breakers too.
One for a shower, one for a fan and one for a shaver unit. :eek:

Only playing, reference a recent thread.

Boydy

You little tinker, can't believe MDJ ended up getting banned but the thread did get a bit heated
 
I had a similar thing on an EICR last year.
3 phase, the link between the breakers was broken, so 2 phases would go off, then you would have to flip off the other one separately.
I wasnt quite sure if I should give this a code.
I asked on the IET forum. The replies were "make an observation, not potentially dangerous".
Think of fuses supplying 3 phases - 3 separate fuses to take out, just like 3 separate CB's.

It isnt good practice to put a new install in with 3 separate CB's, but I cannot see it breaking any Regs.


But it no longer does what the designer of the installation intended.

Boydy
 
I had a similar thing on an EICR last year.
3 phase, the link between the breakers was broken, so 2 phases would go off, then you would have to flip off the other one separately.
I wasnt quite sure if I should give this a code.
I asked on the IET forum. The replies were "make an observation, not potentially dangerous".
Think of fuses supplying 3 phases - 3 separate fuses to take out, just like 3 separate CB's.

It isnt good practice to put a new install in with 3 separate CB's, but I cannot see it breaking any Regs.


Make an observation? - If the 3 separate mcbs are feeding a 3 phase motor and one trips (for whatever reason) then the motor may continue running on the remaining phases ('single phasing') - this can/will cause damage if left unnoticed.
 
Make an observation? - If the 3 separate mcbs are feeding a 3 phase motor and one trips (for whatever reason) then the motor may continue running on the remaining phases ('single phasing') - this can/will cause damage if left unnoticed.

But what if the motor was protected by 3 separate BS 88 fuses as most are would you code 3 That ?
 

Reply to 3phase breaker made of 3 single phase breakers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
556
Hi, searched the forum but cant locate anything similar so apologies if ive missed something. Ive got a new hob to install in the kitchen...
Replies
5
Views
1K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
275
We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock