Hi
i have industrial washing machine originally from Italy which was installed in the UK with a step down trafo from 415v to 380v now the machine is to be installed in Ireland with line voltage of 400v. my question is do i still require the step down trafo, am aware of current and torque changes
thanks
 
Remove it and the nominal voltage
Hi
i have industrial washing machine originally from Italy which was installed in the UK with a step down trafo from 415v to 380v now the machine is to be installed in Ireland with line voltage of 400v. my question is do i still require the step down trafo, am aware of current and torque changes
thanks

If you remove it then the nominal applied voltage will be about 5% high.
Leave it and you will be about 4% low.
Both are within tolerance for 400V nominal but then the 400V is also subject to tolerance. Maybe more likely to be positive rather than negative

On balance, I'd be inclined to leave the transformer in and measure its output voltage when energised.
 
It would depend to be honest on the actual site voltage, like the UK, I suspect the nominal voltage is 400v but in reality it is 415v anyway so leave set up as is IMHO or check the actual voltage before connection at least to repeat what besoeker has already suggested.
 
Last edited:
The transformer might have additional taps you can choose from - 380, 400, 415 is not unusual.
 
rockrose

I agree with all advice given. As it has been fitted with a transformer someone must have assessed that there is an issue with voltage. Without seeing the actual machine, it is impossible to ascertain if that original assessment is correct. If I was moving this washing machine I would:

1. Check the actual voltage range of your current supply. It will be a range rather than a value. If you have access to a voltage analyzer then measure over the usual operating hours of the machine. If you only have access to a multimeter then measure the max, min and mean values over the same period. If your multimeter is not equipped with max/min recording then take a number of readings throughout the day.

2. In January measure the voltage range of supply in Ireland.

3. Assess if any corrective action is required.

Feel free to post your results, along with any manufactures specs on the washing machine.

Good luck
 

Reply to 415v to 380v step down trafo in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
656
Hi all, I am an electrician working for a OEM machinery manufacturer based in Germany, we are the local hub that is now taking over the...
Replies
8
Views
999
Morning all, We are looking at qualification requirements for inspection and testing to BS EN 60204, all of our work is past the main isolator of...
Replies
2
Views
730
We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
753
Hi everyone, I need help installing a Lorex smart doorbell. I have tried to install a doorbell transformer several times to no avail. The first...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock