Discuss 63 amp socket Table 41.1 in the UK Electrical Forum area at ElectriciansForums.net

Pretty much!

2015-05-13 10.47.05.jpg
 
No,

Likelihood of damage to cables.

Rcd are for the protection of persons, not equipment.

Trailing leads, associated generally with plugged in equipment tend to get damaged exposing cores, or potential short circuits.

An example may be a 63A welding set, loads of steel plate being moved around, and potential for dropping plate sharp edge-on to the welder supply cable.

Fixed equipment tends not to be like this.

To me that would mandate RCDs instead of reduced disconnection, but what do I know? ?
 
Alright.

So double checking that would mean a hard wired cooker could get away with 5 seconds, but a flex cooker would require 0.4 seconds? In the US almost all cookers have plugs on them.
Sort of, the cooker example is unlikely to fall within this range (unless industrial, or especially large), but yes there could be loads which are final circuits between 32A and 64A where being hard-wired or plugged in would make such a difference.

In the uk a plug may be used up to 13A on a cooker, above this it is almost always wired in except in a few occasions such as temporary catering where industrial type plugs will be used.

The biggest area to be impacted is industrial as they are likely to have portable/mobile loads that fall in this range.

Essentially as newer versions of the standard are developed the limit of 0.4s and the use of rcds is getting applied to more and more.

I think the whole idea is that eventually all final circuits supplied by a socket outlet should have rcd and 0.4s.

Remember this clause is aimed at final circuits only.

Distribution circuits do not fall under this clause - reflecting the need for discrimination, and the likelihood that when used for distribution it would be controlled by knowledgeable persons.
 
My understanding is that in India, all final circuits are required to disconnect in 0.4 seconds or less. Personally I like the idea.

An exception for 5 seconds is needed for sub circuits though- 60 amp life safety feeder must selectively coordinate with the final OCPDs.
 
My understanding is that in India, all final circuits are required to disconnect in 0.4 seconds or less. Personally I like the idea.

An exception for 5 seconds is needed for sub circuits though- 60 amp life safety feeder must selectively coordinate with the final OCPDs.
India. An interesting place to work with electrics (as I have)...... least said about their 'standards' the better, I feel.
 

Reply to 63 amp socket Table 41.1 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I’m testing some electric meters. As the circuits have no load on them to prove each ct I’ve plugged a hair dryer to simulate a load and...
Replies
3
Views
473
Hi, firstly appologies if my terminology is wrong but I know very little about electrics and have no idea why this is happening - I have 2...
Replies
4
Views
447
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
678
Hi everyone. I am really puzzled by this, but I suppose there is an obvious answer / reason! Anyway, Table I1 in the OSG says the mΩ/m value for...
Replies
2
Views
740
One of our contractors has identified a concern with multiple showers on a single 100 amp supply.(unsure how many yet i have asked for further...
Replies
3
Views
204

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock