Search the forum,

Discuss 6mm incoming earth in the UK Electrical Forum area at ElectriciansForums.net

There is a note in Best Practice Guide 1 (CU changes) that says a 6mm bond on PME can be left in place if it has been there a long time and shows no thermal damage:


3. A 6 mm2 main protective bonding conductor size could be deemed adequate where the minimum size required by Regulation 544.1.1 of BS 7671 is 10 mm2, if the bonding conductors have been in place for a significant time and show no signs of thermal damage
 
Yeah he started of saying he had 6mm earthing conductor.... then we jump all over the place.

But a Welsh man wont the darts on diff channel 180v
 
Definitely a 6mm that's been confirmed funny thing is underneath next to this looks like a chopped earth cable which is much bigger
Yes, I'm rolling back on this.

Here is a 6mm² in relation to my 25mm² tails and 16mm² main earth.
20210531_140835.jpg
 
It's the sort of situation that might result in a Catch 22 unless some common sense is applied.

When you go ahead with the fuse upgrade it is entirely possible that the DNO will demand an up to date electrical certificate for the property to show that everything is in place and suitable for 100A, before they do any work. So then you'd end up in a Chicken vs Egg situation.

In most cases (having carefully assessed the situation) I'd personally feel comfortable with doing as suggested, with 16mm earth from the new board to a block near to the main head (and likewise with 25mm tails to henley blocks connecting to the existing 16mm ).

That would be on the understanding that the earth was to be upgraded (or that the DNO would decide they were happy with existing) - as well testing the existing Ze (test of the level of the current earthing) and a quick check with the adiabatic. I'd upgrade main bonding to 10mm too where it was reasonably practicable to do so.
 

Reply to 6mm incoming earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
961
Hi, I have been tasked with a kitchen rewire. The current DB is fed by a 16mm armoured. There is a split load old contactum DB which I don’t...
Replies
4
Views
1K
In my flat the main earth is the cable pictured below it has 7 strands any idea what size this is? And if it would need to be upgraded for a cu...
Replies
11
Views
2K
Hi guys, I hope you're all doing ok in this heat!! I have recently carried out an EICR on a domestic property where it failed miserably. The...
Replies
6
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock