Discuss 85 amp 220v subpanel in the DIY Electrical Advice area at ElectriciansForums.net

Rex1956

DIY
Reaction score
0
I would like my plan checked by a professional. This project is a semi-open pavilion with a load center approximately 100 feet away. I am rating for 120' to ensure compliance with the NEC. My review of the NEC leads to believe that this will be a damp environment, so I am using an outdoor rated panel.

Wiring is calculated as follows: (3) 3 awg copper THHN/THWN with (1) 8 awg copper bare or insulated ground buried in 2" schedule 4 (schedule 8 above ground) pvc conduit 18" deep. There is no conduit fitting violation of greater than 180 degrees between pull points. The subpanel is not bonded and will have a separate grounding bar and 8 awg ground wire to (2) 5/8" x 8' stainless steel grounding rods not closer than 6'.

Thanks in adavance for any words of advice or caution. As an ancillary matter this project is in western NY, Niagara County. I know how NY state loves its regulations, so if there are any other cautionary measures, please advise.
 

Reply to 85 amp 220v subpanel in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi! I’d like to install a pedestal-mounted (230 V, 30 A max - programmable) EV charger close to my driveway, which ends about 12 feet away from...
Replies
1
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock