Surely the only 'proper' way of doing it is 6mm cable, 45A breaker, Ref method C throughout.
That way Ib is less than In.
?
That way Ib is less than In.
?
Discuss 9.5 kw shower on 6mm ? in the UK Electrical Forum area at ElectriciansForums.net
if it ain't broke, don't fix it. perfectly OK with a ccc of 47A on a 40A MCB.
Surely the only 'proper' way of doing it is 6mm cable, 45A breaker, Ref method C throughout.
That way Ib is less than In.
?
can you get a 45A, 5 minute time switch?47A is the absolute max under continuous clipped direct conditions with no VD. I personally wouldn't put 6mm on a 40A MCB, nor run a 9.5KW load on it, but that's just my opinion.
As far as not being in the shower for more than 5 or 10 mins goes.... tell my daughter that.
Ive seen a 9kw shower ran on a 32 amp MCB
well, if you insist on using your 6mm for the loft light, you'll have to use 1.5mm for the shower as you'll have no 6mm left.lol nope but i did she a shower not sure what the kw rating was ran off a 30 Amp BS3036 fuse in 1.5mm 3 core!!!
At first glance i thought it was 4mm, looked in the loft and it was all melted under the insulation.
Still worked though i found it as i was installing a loft light.