Surely the only 'proper' way of doing it is 6mm cable, 45A breaker, Ref method C throughout.

That way Ib is less than In.

?
 
if it ain't broke, don't fix it. perfectly OK with a ccc of 47A on a 40A MCB.

47A is the absolute max under continuous clipped direct conditions with no VD. I personally wouldn't put 6mm on a 40A MCB, nor run a 9.5KW load on it, but that's just my opinion.

As far as not being in the shower for more than 5 or 10 mins goes.... tell my daughter that.
 
47A is the absolute max under continuous clipped direct conditions with no VD. I personally wouldn't put 6mm on a 40A MCB, nor run a 9.5KW load on it, but that's just my opinion.

As far as not being in the shower for more than 5 or 10 mins goes.... tell my daughter that.
can you get a 45A, 5 minute time switch?
 
lol nope but i did she a shower not sure what the kw rating was ran off a 30 Amp BS3036 fuse in 1.5mm 3 core!!!

At first glance i thought it was 4mm, looked in the loft and it was all melted under the insulation.

Still worked though i found it as i was installing a loft light.
 
lol nope but i did she a shower not sure what the kw rating was ran off a 30 Amp BS3036 fuse in 1.5mm 3 core!!!

At first glance i thought it was 4mm, looked in the loft and it was all melted under the insulation.

Still worked though i found it as i was installing a loft light.
well, if you insist on using your 6mm for the loft light, you'll have to use 1.5mm for the shower as you'll have no 6mm left.
 

Reply to 9.5 kw shower on 6mm ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi, Same project as detailed in my other post (I want to run shower cables to the CU whilst the kitchen ceiling is disturbed). I'm going to...
Replies
5
Views
3K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
213
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K
I have a TPN board that will feed 8-10 sub boards. The loads on each board are negligible 5-10 amps peak but mostly 1-2 amps. The distribution...
Replies
26
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock