Hi, While carrying out a periodic inspection I came across a 9kw shower on 4mm cable, 40A type B ocpd, 30ma rcd.

I have given a code 3, for the following reasons;

1. No sign of thermal damage at any termination.
2. Shower cannot overload as fixed load.
3. Short Circuit & Earth loop impedance well within limits.
4. Shower will not run at maximum 9kw.

I have also noted to the customer that the manufacturers recommend a 10mm cable. I would just like your opinions on the above.

Cheers
 
i would have been tempted to clamp the load, see what it actually pulled. but i think C3 is right.
 
im a trainee but surely 4mm is too little for 39A or 37.5A on 240volts. the cable is in a wall isnt it?!? and i thought showers will always use the load thats stated...

9000/230 = 39.13

9000/240 = 37.5
 
Hi, While carrying out a periodic inspection I came across a 9kw shower on 4mm cable, 40A type B ocpd, 30ma rcd.

I have given a code 3, for the following reasons;

1. No sign of thermal damage at any termination.
2. Shower cannot overload as fixed load.
3. Short Circuit & Earth loop impedance well within limits.
4. Shower will not run at maximum 9kw.

I have also noted to the customer that the manufacturers recommend a 10mm cable. I would just like your opinions on the above.

Cheers

Hmm guess again.
 
im a trainee but surely 4mm is too little for 39A or 37.5A on 240volts. the cable is in a wall isnt it?!? and i thought showers will always use the load thats stated...

9000/230 = 39.13

9000/240 = 37.5

Yes you are quite right that a shower should be considered at its full load as, without disconnecting one of the heating elements in the shower, you can't guarantee that it will be run in half power mode.

Your second current calculation is right, the first one is not quite there. (I'm assuming the 9kW is the 240V rating)
If you look at the rating plate on a shower (or anything else) you will find that it has a different rated power at each voltage.
The power dissipated by a load is determined by the electrical resistance and the voltage applied across that resistance. As the resistance remains constant a change in voltage will result in a relative change in power.

As a result the current at 230V will be a bit less than that at 240V.
 
The heating element will always run at 9kw its the speed of the water passing through it that governs the heat

its not like diversity on a cooker!!!!

What install method?

c2 for me
 
It probably started out as a 7KW or even less when first installed, it also worries me that the big DIY chains are always promoting 10.8KW showers, ridiculous power rating IMO !
 
What type of cable? 4mm 90 degree should be ok depending on installation method.

Welcome to the forum JBL..

Just in response to your post - how will it be sufficient if the equipment it is connected to will more then likely be 70c rated thus you would have to add a derating factor to the cable.... always take your CCC values off 70c rated cables unless your working with high temperature equipment including connections.
 

Reply to 9KW Shower on 4mm cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

At a bread and butter job, loose socket, socket not working, change two lights. Sticking out rather like a sore thumb was this (I removed the wire...
Replies
5
Views
2K
At work in our main kitchen, the 6kW (26A sp) water packed up. The restaurant staff were in turmoil, as they had no hot water to make the tea...
Replies
21
Views
3K
Another what code! This is in conjunction with an EICR I have just carried out. 9.5kW shower on 6mm and 32A MCB. Been in place for a long time...
Replies
8
Views
3K
Doing an inspection and came across this. Feeds are as follows: Cutout to Meter - 25mm Meter to connector blocks - 25mm Connector blocks to...
Replies
64
Views
6K
Hi. This is a gloriously messy installation I looked at this morning at a house a friend just purchased. It t became quickly clear it was more...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock