table 1b appendix 1 p(97) OSG for diversity allowances.......
Discuss A lighting CB wont re-set and shower CB rating query. in the Australia area at ElectriciansForums.net
so you are using 10mm cable...ok....nothing wrong with a 40A mcb for this circuit as i have already said......wont be used at full pelt....or if it is..it wont be for long...owch!!and what does that say
as your saying that a 9.5 kw shower in use including voltage drop does not run over 40 amps
so did you ask the inevitable question.."have you had any work done sinse i was here last"?.....IR mate on the offending circuit......at the board first to verefy theres either a short circuit or a breakdown in insulation and remember to disconnect anything electronic being fed from this circuit first wont you mate as you could fry it..lol....Cheers for the quick replies. I need to check it was a 9.5kw because something made me go up to the 50a rather than the 40a. It may be that it was a 10.5 but I haven't got my notes to hand. If I phone them they won't know either. I used this for my assessment and nothing was mentioned then.
Any tips on the lighting circuit as, if I have to go, it'll have to be done in a day, as I haven't the time to stay longer. Not looking forward to this as it's a 5am start and won't get back to 9-10pm depending on what needs to be done.
well this is the thing David.....Our 9.5 kw mira pulls 34 amps when its turned to max! Always has done