Hey guys, First time user here. 2nd year electrical apprentice down under! Need help and guidance with a question i've been tasked with here. Don't neccersarily need the answer to the question but any guidance into it would be helpful.
Question is 'You have a three phase induction motor (415V) rated at 240nm. It is connected to An auto tranformer starter that starts at 70% supply voltage. What is the torque developed at start up? Show any working out?
 
Does this help you? I will let you study my scribbles and if they do not make sense come back to me. The key things to know are (1) at locked rotor when the torque is 240Nm at 100% Vs the induction motor is acting as a transformer with an N to 1 turns ratio between stator and rotor and (2) the force F between the stator and rotor is proportional to the product of the stator and rotor currents Is x Ir and (3) the torque T is proportional to the force F and (4) the stator current is Vs/Z where Z is impedance the supply sees looking into the motor .

PS: I ignore magnetization current and transformer core losses.

Forces Between Parallel Conductors – Learn – ScienceFlip - https://www.scienceflip.com.au/subjects/physics/electromagnetism/learn4/#:~:text=When%20two%20wires%20carrying%20a,carry%20currents%20of%20different%20magnitudes.

Equivalent Circuit for an Induction Motor | Electrical4U - https://www.electrical4u.com/equivalent-circuit-for-an-induction-motor/
 

Attachments

  • 88B4C262-1A65-4F80-A4E5-10B9D62C52AB.jpeg
    281.6 KB · Views: 10
Last edited:
I should have written Es x Is = Er x Ir, and then Es/Er = Ir/Is = N. The equivalent circuit assumes the transformer is perfect with its resistance and reactance and losses as lumped components connected to it externally. This correction does not alter what follows in my analysis.
 

Reply to AC Motors & Transformers Question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
737
Hello, my name is Kelvin. I'm a trainee hydraulic engineer in Indonesia. I apologize if this question has been answered before / if this question...
Replies
2
Views
1K
Hi all, For clarity, I'm not a qualified electrician, but have a reasonable amount of experience as I've done plenty of wiring (signed off by a...
Replies
19
Views
3K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
789

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock