Discuss addition to ring in the UK Electrical Forum area at ElectriciansForums.net

Sounds like a N to E fault somewhere - and not necessarily on this socket circuit.

Some additional information might be useful - what did "all tests" consist of, and what actually were the test results that were "good". And a description of the board configuration would be helpful.
 
As above more info required You could of trapped a neutral at one of the new socket or when you pulled the new cable in you could of burnt the cable against another one or there may be too many appliance now with high earth leakage on the circuit, did you get good IR results
 
As above more info required You could of trapped a neutral at one of the new socket or when you pulled the new cable in you could of burnt the cable against another one or there may be too many appliance now with high earth leakage on the circuit, did you get good IR results



end to end figure of eight IR >999
L 0.74 L cpc 51.2
N 0.74 N cpc 72.3
CPC 1.04
 
The way you have wrote the reading do not read correctly

I think you mean Ring reading

Live to live 0.74
Neutral to Neurtal 0.74
CPC to CPC 1.04

and IR test
IR >999 Live to live L cpc 51.2 and N cpc 72.3

Does the RCD test OK with nothing connected
 
Is there any load on the ring circuit ,
How have you installed the new cable ( if they are with other cables the could be burnt together when pulling them in) May be worth doing IR between the ring and other circuit if this is the case
Have you checked you have noted snaged a neutral when pushing sockets back
 
So either the appliance you have plug in has a high earth leakage coursing the RCD to trip or buy putting load on the circuit the insulation some were is braking down coursing the RCD to Trip
 
I would hazard a guess that as the RCD holds up when the N for the RFC is disconnected, and it was OK before, it's something you have caused, check from the points of addition.
 
Perhaps just the neutral in the wrong neutral bar of the CU. It does depend on whether it trips in tens minutes after power on or whether it trips at once when current is drawn.
 

Reply to addition to ring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

When altering / addition to an existing circuit and the RCD is a type AC but you notice DC components within that circuit do you upgrade the RCD...
Replies
0
Views
349
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
860
Calling all electrical professionals / boiler tradesmen -WE NEED YOUR HELP! Every so often (twice in the last two days) when running the hot...
Replies
15
Views
534
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock