Section 443 although mentioning switching of equipment within the installation actually only covers atmospheric overvoltage in the description.
Depending on the meaning "operation" could mean automatic or manual operation; in the case of automatic operation the overcurrent not the overvoltage is the protection this device is providing.
Motors running and voltage recovery could also lead consequentially to overvoltage against which protection presumably should be provided but again not covered by 443.
Therefore c is the most appropriate response even though the others could be considered relevant C is the most relvant.