Hi
I wired the first fix upstairs in a new house 2 years ago and am now returning to carry out the second fix.
On the lighting radial I have been using a fluke multi meter to check the resistance from ceiling rose to celing rose as I go along to check that all is good with the connecting 1.5mm T&E.

All seemed fine fine until the 3rd rose along, 1 live was 0.7 ohm (obs from the previous rose) but the next line (which shouldn't be connected to anything) gave 4Mohm with ref to the previous rose.

I tried a seperate test from the next un connected rose to the next rose after that (just the cable, not terminated) and the resistance showed 40Mohm spuriously.
It would be 40 M one sec the OL then I would touch the probe with my hand and it would jump back to 40M or 50M.

Has anyone come across this? The house is dry and I'm pretty sure no cables were squashed etc since the 1st fix but I ready don't want to start cutting plaster to try and find a fault if there isn't one there.

Thanks

JT
 
I connected my meter at the unterminated live wire at the fuse board and using a long piece of wire and multimeter I checked the cable at the 1st rose to make sure that that was the 1st rose (resistance = 0.4ohm). I then connected the meter to the next cable at the 1st rose and checked the resistance to the 2nd rose to make sure that was the same cable. Again under 1ohm. The meter is on auto range resistance mode.
On the third rose the cable coming from rose 2 again was less that 1 ohm but the other cable that travels to rose 4 and is unconnected read 4Mohm while the other end of the Meter was still connected to rose 2.
 
I wonder if your test leads are faulty. Connect them together and observe the Ohmmeter as you you wriggle the test leads along their length. This is what I once found with my test leads.

I assume you are testing cable links between CR positions, but no actual CRs wired in yet. Or, are you working away along the radial from the DB and wiring in a CR and then taking measurements?
 
Last edited:
I wonder if your test leads are faulty. Connect them together and observe the Ohmmeter as you you wriggle the test leads along their length. This is what I once found with my test leads.

You would expect faulty test leads to give a higher value than expected, not lower
 
2 years is a long time between 1st and 2nd fix, a lot can happen to those cables in that time. someone else could have re routed them for you.
 
Hi dude,you obviously have a poor connection between your test points,but whether this is due to damage,poor jointing or alteration...who would know...

I would suggest a further poke about,before livening up,and re-testing with the appropriate test equipment. Good hunting:artist:
 
Hi dude,you obviously have a poor connection between your test points,but whether this is due to damage,poor jointing or alteration...who would know...

I would suggest a further poke about,before livening up,and re-testing with the appropriate test equipment. Good hunting:artist:

Poor connection? He's getting a reading between two points which are not supposed to be connected at all.
 
By Marconi I have enjoyed pondering this problem but you no doubt might be frustrated with it. It is not completely clear to me whether you are simply taking continuity measurements on unconnected lengths of cable runs or end-to end on a growing length of cable run as you wire in the CRs. So I have assumed the former but what I am about to write applies to the latter as well.

A digital multi-meter, when set to measure resistance, does so by injecting a constant current through the circuit under test and then measuring the voltage across the circuit. Using Ohm's Law it then calculates the resistance of the current's path. As the resistance of the circuit under test increases, the injected constant current is reduced. This is because the DMM is both battery powered and for safety the applied voltage is limited to around 10 Volts. With the meter you are using the resistance scale is automatically changing up or down, so in turn is the injected constant current. By choosing the inject current to be 1, 0.1, 0.001 mA etcetera for example a straight voltage reading is the same numerical value as resistance for an applied emf of 10Volt - 10k, 100k, 1000k Ohms etcetera

Now let us think about your test arrangement. You are using one short test lead and one long wandering lead. These are connected to the part of the lighting radial circuit you want to test for continuity. These long leads form an aerial and which will pick up electro-magnetic radiation. A small alternating current will flow - micro-Amps - but comparable to the injected current on its higher resistance scales.

There are inevitable capacitance effects which albeit small need charging and discharging. Since the injected current is small on the higher range scales there is a settling time before reliable measurements may be taken.

The connections you make for a test - using your crocodile clips, test lead plugs, bared conductors , dirt- may be covered in grease, dirt, dust and oxidation. Not only do these act as resistive layers, they can also act in a non-linear way akin to a diode. (Railway signalling systems using the track and train wheels suffer from this especially in autumn). This is another interference mechanism to the injection current especially at higher resistance scales.

Before a current - a flow of electrons - can take place between metallic surfaces the so-called wetting current must be exceeded. For switch contacts carrying small currents a capacitor is sometimes connected across them which is discharged when they close to boost the wetting current.

There are then a number of electrical effects which make the DMM unreliable in your test rig when operating on the higher resistance scales. I suggest you only use the DMM for continuity and select an instrument with a higher applied voltage and current to measure higher resistance ; I do not know if the MFT does but the earlier poster recommends its use.

I hope this helps. :)
 
Last edited:
Very in depth reply from Marconi as usual there :) I would do as he and Hellmooth suggested, and use the low ohms range on an MFT. The MFT will use at least 200mA drive current which will help to avoid spurious readings. Unlike your multimeter, which will have tens of Megohms input impedance, and therefore be too sensitive for the type of test you are carrying out. Daz
 
Great answers! Thanks for the input.

marconi, you are correct. I have disconnected any terminations I had and am measuring individual lengths of cables.

I continue to to see what I was seeing while retesting this morning with a fresh head. I am planning to use a megger next week to test with higher voltage but am stating to suspect capacitance, inducted voltages from parallel runs or antenna interference as being a factor.

Will post after I have carried out the megger test for future reference.

Thanks again

JT
 

Reply to Advice on meter readings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Looking for DIY electrical advice. I have 7 x spots, and each are fitted with 1 x T&E connector block fitting [see photo]. In the past...
Replies
3
Views
655
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
439
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
I am fixing an old BM223 for myself and have done well so far, got it a new battery holder, found the 12v zener shorted and a 1N4007 o/c next to...
Replies
0
Views
365
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
862

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock