Hi,

I am currently getting quotes together from various sparks that are Part P compliant for wiring up a new outdoor CU to power a 43A tub.

For those that are in the know what installation method would be preferred/advised?

a. New SWA cable run from meter around the house to new CU? What size cable 16mm or 25mm?

or

b. Take feed from existing CU MCB to feed secondary CU unit

or

c. Any other options.

Thanks
 
Why do you think this hot tub requires a CU for itself at the load end ?
Yes SWA cable would usually be the most appropriate method.
The cable size would depend on the load requirements of the hot tub, subsequent cable calculations, and the manufacturer's installation recommendations. 16mm sounds way to big though for a load of 43A.
 
Why do you think this hot tub requires a CU for itself at the load end ?
Yes SWA cable would usually be the most appropriate method.
The cable size would depend on the load requirements of the hot tub, subsequent cable calculations, and the manufacturer's installation recommendations. 16mm sounds way to big though for a load of 43A.

Main reason is for future proofing, eventually I'll have some garden lighting that I will want to run too, so having a separate CU would prevent the main CU RCB's from tripping if a ground fault occurs. I was thinking 16mm or higher only because it was the feed to the CU, If I can get away with less then excellent.
 
nah, it's fitting unnecessary CUs to boost holiday funds.
 
Main reason is for future proofing, eventually I'll have some garden lighting that I will want to run too, so having a separate CU would prevent the main CU RCB's from tripping if a ground fault occurs. I was thinking 16mm or higher only because it was the feed to the CU, If I can get away with less then excellent.

As Risteard says, take advice from the electricians quoting for the work. If you don't trust their opinion then don't deal with them.
Cable calculations will have to be carried out with your prospective full demand for the circuit before any cable sizes can be arrived at, as well as your existing installation assessed for suitability of this proposed expansion.
 
As Risteard says, take advice from the electricians quoting for the work. If you don't trust their opinion then don't deal with them.
Cable calculations will have to be carried out with your prospective full demand for the circuit before any cable sizes can be arrived at, as well as your existing installation assessed for suitability of this proposed expansion.

Quite difficult to trust an opinion if you don't know whether your sparky is trying to "boost holiday funds" or cutting corners by spurring of an existing MCB. But hey ho, thanks for your opinions either way. Appreciate your time.
 

Reply to Advise on additional CU for hot tub in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
688
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
1K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
975

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock