EICRs for rentals have only been a requirement for a few months now, there's a good chance there are no previous records available.Date of last inspection -Being a PRS property and (I'm led to believe) the client has used the same people every time - Records should be available right?
This would be evident at the MET and by testing. There would be 2 X 6mm singles in the earth bar. Disconnect and continuity test each to the pipework would confirm. Similar test for earthing conductorMain protective earthing conductor is recorded as 16mm with 6mm main bonding conductors. I take umberage with them being verified as I don't believe this was done (certainly if you look at the under-sink shot I posted in #earthing-and-bonding , it's just a link across the water meter, with no further signs of bonding (haven't checked boiler).
This is listed as 16mm. Worst case, run adiabatic using the PFC and a 100A BS1361 (the max expected in domestic), then check 544.1.1. It should comply at 10mm.3.4 confirmation of earthing conductor size - 542.3 543.1.1 - ticked but as DNO OCPD not verified can't say if 6mm is appropriate or not.
A tough one. A lot of sparks (there are at least a few on this forum) don't use torque drivers, and the torque data is rarely available on the board itself.4.21 connections tight and secure - Not a torque driver in sight, yet ticked
Probably wouldn't use a torque driver for tightening terminations at accessories. I never have, and don't recall seeing manufacturer's data for such.5.17 terminations (526.6) ticked but not a torque driver in sight
RCD protection on all circuits serving the bathroom, main bonding confirmed? Sup bonding not required.6.4 Supp Bonding not present/verified but marked N/A
Other than that, mostly agree with your comments. It's not a great report. Have you noticed any C1s or C2s that the inspector may have missed?