Discuss AM2 help Selection of Circuit breaker in the UK Electrical Forum area at ElectriciansForums.net

M

mcbarber

Hi guys,

Need some help on selecting a circuit breaker for a 3 phase motor on a DOL starter for my AM2.

This is how far I have got let me know how to complete my calculation.

Information I know; Its a 1kw motor
Its wired in singles in trunking to the DOL starter, Then in 1.5mm SY
to the motor.


1000/(1.73x400) = 1.45A

To me 1.45A dose not seem correct, I know it would be a type C breaker as of the large current when starting. If anyone could help that would be great.

Cheers Matt
 
Consider:
What does the 1kW represent - input or output power?
What is the power factor of a typical 3-phase motor?
How should the MCB rating relate to the running current and the locked-rotor current?
What device is providing the overload protection?
 
hmm I'm getting a little confused, I haven't had any experience in this so trying to tech myself.
Is there any chance someone can break it down for me how to do it?
 
As its for the AM2 I would assume that 1kw in the power input of the motor as your only concerned by that for cable sizing etc.
The calculation would be 400\1.73.
Try that and see if it makes more sense.... :)


Sent from my iPhone using Tapatalk
 
the 1.443418014 is the current

Given the limited precision of the input values, I would not try to quote the result to the nearest nanoamp! But yes, 1.4A is what you get disregarding efficiency and pf.

FWIW, a 1.1kW motor (1.5hp in old money) will have a line current in the order of 2.7A on 400V.
 
Ok so, I then try and select my circuit break from this info.

Iz >= In >= Ib
2.7A>= In >= 17.5A

does this mean I could use a 6A TYPE C MCB
 
Its a sticky area is this and I don't want to throw confusion into the works but what your taught about motors and inrush currents etc at college isn't really worth the paper its written on, its so brief and concise that it gives little prep' for the real world of motor control and protection. If this is a standard 400v 3ph induction motor with a normal starting duty on DOL then using Schneiders Tech' data sheets you can use a number of options for protection, in this particular case they state a 6(B), 6(C) or 4(D) will all be adequate and only your permitted zs would limit you but been so small an mcb then I don't see that even been an issue.

The misconception that type B, C and D are relative to certain inductive products is misleading, the tripping curves are different which allows for different inrush values and once you know this then you can determine if the inrush of the inductive load you have may require a higher breaker type or value, it is sometimes the case that a type (B) can be used like above but what you college is looking for maybe different and they maybe looking for you to spec' a type (C) as that's what they usually teach you a C is used for.
 

Reply to AM2 help Selection of Circuit breaker in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello. So, I would like to know how I can choose the correct circuit breaker value when doing a new installation. My example is: I have 16...
Replies
2
Views
872
I have my AM2 coming up next week but something is puzzling me and I’m hoping someone can help me out. So there is some SY cable coming out of...
Replies
11
Views
2K
Summary (TL;DR) Several lightbulbs in my home supplied by one circuit breaker dim over time and go out in about a year. Right now, the ceiling...
Replies
0
Views
732
Background Two weeks ago, lightning struck a tree in our yard. Many circuits tripped and several electronic devices failed. There was a strong...
Replies
2
Views
874
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
864

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock