Discuss Am2s Continuity Of Protective Conductors in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

A continuity test by disconnecting both ends and testing end to end to get a resistance. I’m not sure if I need to add this to the test sheet as a circuit or just tick a box on the schedule of results it’s for my am2s end point assessment

When we link out certain conductors, or use a wander lead to test continuity, what are these tests normally known as?😉

It’s all ready on the schedule of test results.
 
@mpratt263801 ,

The point we're both making is this, there are two tests you can use to establish whether or not the CPC is continuous. These are commonly referred to using the results they provide, which is the R1+R2 test (typically performed by linking L+CPC at the board and then taking a resistance reading at each point on the circuit and recording the highest value - Ring finals is different and you get the R1+R2 during the figure 8 testing) and the R2 test (typically performed by connecting a wander lead to the earth bar in the board and then going to every point on a circuit and taking a resistance reading to the CPC connection and recording the highest value).

The results from these tests have their own result columns on the schedule of test results.

But I'm also thinking this could be the same confusion I recall... I'm honestly not sure of the source of this question, I think it was my AM2, but I'm not 100% certain... I recall being asked a question along the lines of 'What are the results of the CPC continuity tests?' and there just being like a blank space... no table, just a place to write. The answer I gave went something along the lines of 'The CPC of all circuits is continuous as demonstrated by the R1+R2 results obtained for them on the schedule of test results (there are no open circuits and the results appear to be in the expected range)' or something like that. I also remember being somewhat confused about what they were expecting.
 

Reply to Am2s Continuity Of Protective Conductors in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi question whats my best route ive just done the am2 and past my nvq has expired as i took a while before completing the am2 i have level 2...
Replies
24
Views
2K
Hi got my am2 Tomorow and not sure on how to test continuity for 3 phase circuits, like where to link out also for IR test aswell
Replies
0
Views
1K
Hi all. I recently failed a section of my AM2E assessment. Passed 7/10 but failed on some silly things I'm confident of correcting second time...
Replies
1
Views
368
resitting Saturday my am2 4 sections a3/b/d/e swa and sy failed on protective conductors on both swa i under stand thats the earths i...
Replies
1
Views
1K
I recently just done my AM2 resit and in my inspection and testing, despite the invigilator watching me do the tests, I think I may have forgotten...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock