Discuss AMPAGE TESTING (12 Volt DC) in the Australia area at ElectriciansForums.net

S

srands

Useful reference guide for AMPAGE TESTING of 12 Volt DC.

AmpageTesting12VoltDC.jpg

PICTURE VERSION URL:
https://blufiles.storage.live.com/y...znmbCQXpJVytYH2xzFs/AmpageTesting12VoltDC.jpg


WORD VERSION URL:
https://skydrive.live.com/view.aspx?cid=9EC5688DD90EEC6C&resid=9EC5688DD90EEC6C!581

TOOLS NEEDS:
MULTIMETER, SCREWDRIVERS & BLOCK CONNECTORS

This is quite simple see following pictures (Much easier to do then first impression on reading instructions), the MultiMeter in this instance (DRAWN, POSITIVE TERMINAL) tests the AMPAGE between the POSITIVE SUPPLY (red probe lead) and the POSITIVE LOAD (black probe lead). Hence the NEGATIVE is uninterrupted from SUPPLY to LOAD (In other words, leave it alone). In this instance the positive supply has croc clips, normally I'd use insulated BLOCK CONNECTORS:
PIC1 (multimeter measuring AMPAGE between POSITIVE supply & POSITIVE load)
MultiMeterAmpTestDC12V.JPG
PIC2 (12V dc Battery Charger powering car cd player, with MultiMeter Testing AMPAGE)
MultiMeterAmpTestDC12vPoweredByBatteryChrgPlayingCarcdPly.jpg
PIC3 (CAR CD PLAYER in house install powered by CAR BATTERY CHARGER 12 V dc 4A)
CARcdPlayerPoweredByBatteryChrg12Vdc.JPG
PRECAUTIONARY NOTEs:
~ Obviously the NEGATIVE and POSITIVE can NOT touch each other (Neither SUPPLY or LOAD)
~ If your MultiMeter has NEGATIVE READING, then means you have your PROBE LEADS the wrong way (Or just ignore the negative symbol, as the AMPAGE figure will be accurate).
~ The 12V dc MOTOR/PART or ALTERNATOR/SOLAR PANEL may CHARGE/DRAW a greater AMPAGE/CURRENT then the capacity of the MULTIMETER & its LEADS (At this point the actual ampage is unknown). For example most car electrical parts are low current (Indicators, elec windows, elec sunroof, heater, etc), with the obvious exception of a car starter motor (Extremely high ampage/current, totally unsuitable for testing with MultiMeter). Hence if the 12V dc part/motor or the charge rate of the power supply is greater then 10A this may melt your MultiMeter probe leads and/or break the MultiMeter (Unless you have a 20A DC MultiMeter! Obviously the ampage max of those is 20A DC).

OTHER NOTES:

~ The AMPAGE reading given by your MULTIMETER, is given by testing 'A' POSITIVE or 'A' NEGATIVE, however the AMPAGE reading is the total AMPAGE drawn/charged, so this figure should NOT be doubled in your calculations.

~ If you're testing direct from a car battery and it's loom, it may have other parts/motors draining ampage, such as indicators/wipers, etc. So turn ON the ignition (WITHOUT STARTING THE CAR, as the ampage drain would be far too great for the MULTIMETER & PROBE LEADS!), then make a note of what the standard ampage drain is approximately (i), then turn on the motor/device/appliance you want to test (ii). Then subtract the standard ampage drain from the new figure with the appliance/device/motor on to EQUAL the difference (iii) i.e. The ampage of the motor/part etc.
FOR EXAMPLE:
i) STANDARD AMPAGE DRAIN = 0.5a (Car alarm or something else)
ii) STANDARD AMPAGE DRAIN & OTHER MOTOR = 1.5a
iii) CALC 1.5a - 0.5a = 1.0a

Alternatively (my preferred practice/method) connect new leads to the battery terminals, so there won't be any other registered ampage drawn from the car battery. So the ampage reading is what it is!
PS. Don't mess about from behind the car fusebox, keep it simple, either direct from car battery and loom OR new power leads from car battery to motor/part/device/appliance your testing with a MULTIMETER.

I made this guide as a quick reference when testing 12 Volt DC circuits with a MultiMeter, EITHER:
~ ampage CHARGE to batteries
OR
~ ampage DRAWN from batteries.The main reason for this guide is that I was not impressed (And continue to be not impressed with the lack of meaningful instructions) with uncomprehensive manuals supplied with most MultiMeters. Seems odd to make a great feature but don't explain in the instructions.

Remember most MultiMeters (£10 Maplin job ok) only test upto 10A 12V DC, more expensive MultiMeters (UNI-T from Maplin £30 why spend any more) test upto 20A 12V DC.

ALTERNATIVELY To test AMPAGE of 240 VOLT APPLIANCES use a plug in ENERGY MONITOR (From Maplin).

This guide I'm sure will be a great help to test 12 Volt DC circuits, however please feel free to add these links below (Website addresses, urls, etc), the numerous number of posts on this subject (That I couldn't find), and web references to wiring regulations, and any other derogatory negative remarks you have as well!

CHEERS, AND BELOW IS A FULL LIST OF MY OTHER USEFUL GUIDES & SPREADSHEETS (Top entries of electrical interest)

STEPHAN RANDS
AMPAGE TESTING (12 Volt DC)
RING AMP AUTOCALC: 1ST TAB
LIGHTING CIRCUITS, RING & RADIAL wiring diagrams
UTILITY ENERGY MEGACALC
MPG
METRIC AUTOCALC
PERCENTAGE CALCULATOR AUTOCALC
EXCEL USEFUL FORMULAS
MTB ROUTES IN/NEAR HULL, HUMBERSIDE
TIER 4+ CATEGORY TYPE
TIER 4+ MONEY TYPE
AUTOCALC WEBSITE










 
Last edited by a moderator:
Oh dear! Not again! Another of your perverse creations, a solution looking for a problem. For somebody who wishes to provide electrical information for the ordinary person you have a unique, blinkered way of going about it. You can't even get the terminology correct, despite earlier advice on this forum by various members. Far from achieving your object, most of it's over complicated, ill-informed pseudo-science and sophistry. Why you wish to post such tat on this forum escapes me, maybe it gets you some extra hits on your website by association. It is extremely unlikely that you will get support and good revues for your work from intelligent electricians on the evidence presented to date. We have better things to do with our time, like helping those that have genuine problems or who wish to learn from us. You do not appear to fit in to either category. I suspect you post just to blatantly publicise your website and views.
 
Last edited by a moderator:
Oh dear! Not again! Another of your perverse creations, a solution looking for a problem. For somebody who wishes to provide electrical information for the ordinary person you have a unique, blinkered way of going about it. You can't even get the terminology correct, despite earlier advice on this forum by various members. Far from achieving your object, most of it's over complicated, ill-informed pseudo-science and sophistry. Why you wish to post such tat on this forum escapes me, maybe it gets you some extra hits on your website by association. It is extremely unlikely that you will get support and good revues for your work from intelligent electricians on the evidence presented to date. We have better things to do with our time, like helping those that have genuine problems or who wish to learn from us. You do not appear to fit in to either category. I suspect you post just to blatantly publicise your website and views.

Or, in another word ...... SPAM !! :dead:
 
quote
Useful reference guide for AMPAGE TESTING of 12 Volt DC.

Here you go again
I only got as far as line one,but if you insist on referring to the long word for amp,then at least give the guy Ampere some credit and refer to it as amperage not ampage

This is ampage Flash Intro Page
 
Oh dear! Not again! Another of your perverse creations, a solution looking for a problem. For somebody who wishes to provide electrical information for the ordinary person you have a unique, blinkered way of going about it. You can't even get the terminology correct, despite earlier advice on this forum by various members. Far from achieving your object, most of it's over complicated, ill-informed pseudo-science and sophistry. Why you wish to post such tat on this forum escapes me, maybe it gets you some extra hits on your website by association. It is extremely unlikely that you will get support and good revues for your work from intelligent electricians on the evidence presented to date. We have better things to do with our time, like helping those that have genuine problems or who wish to learn from us. You do not appear to fit in to either category. I suspect you post just to blatantly publicise your website and views.

It's simple knowledge, in 12 Volts DC there is no other way. Don't be so negative.

MATE elec is simple, chit chat here is just to confuse novices looking for basic knowledge.
240v ac to find out appliance AMPAGE or WATTs, look at the back of the appliance, look in the manual, or browse the internet. If it doesn't mention AMPAGE or WATTs anywhere (The fuse size may not be a good indication), then use a PLUG IN ENERGY MONITOR (Because there is no other instant alternative, OR use an elec meter just for the sole purpose of testing for power consumption in WATTS/AMPs).


12v dc to find out the AMPAGE or WATTs of a device/motor (Car cd player, car sound amplifier, portable dvd player, etc) look at the back of the device, look in the manual, or browse the internet. However it is more then likely it won't mention AMPAGE or WATTs anywhere (The fuse size may not be a good indication), hence you a MULTIMETER as given in the instructions of the 1st post.
Also a car elec is from a 12Volt car battery hence supply is direct from the battery terminals, or alternatively from the car's CIG LIGHTER SOCKET (If it has 1), since device manufacturers don't make a 12V dc Energy Monitor that plugs into the car cig lighter socket, there is no other alternative to find out the 12V dc AMPAGE of a motor/part.
To calculate correct FUSE from appliance WATTS:
W = Watts, V = Voltage, A = Amps
W / V = A Eg 1200Ws / 240v = 5A

To calculate WATTS max for circuit:
A x V = W Eg 32A x 240V = 7680Ws = 7.68KWs
1000 W’s= 1 KiloWatt (Used on elec meters)

It is that simple, all other chat is just to deliberately confuse, under the false pretenses of thinking they wouldn't be able to do it.
 
Be honest though there is not a socket wire in sight.

Also a car elec is from a 12Volt car battery hence supply is direct from the battery terminals, or alternatively from the car's CIG LIGHTER SOCKET (If it has 1), since device manufacturers don't make a 12V dc Energy Monitor that plugs into the car cig lighter socket, there is no other alternative to find out the 12V dc AMPAGE of a motor/part.
 
Last edited by a moderator:
quote
Useful reference guide for AMPAGE TESTING of 12 Volt DC.

Here you go again
I only got as far as line one,but if you insist on referring to the long word for amp,then at least give the guy Ampere some credit and refer to it as amperage not ampage

This is ampage Flash Intro Page

MATE in 12V or car speak, the abbreviation AMP to most people means AMPLIFIER, hence why I used the WORD "AMPAGE" instead of AMP, no auto electrician sayes "AMPERE" or "AMPERAGE", they say AMPAGE or AMP, but to car drivers, they would/may/might confuse this with car AMPLIFIERS. Hence they'd get confused about power watts and sound watts, hence the substituted full word AMPAGE, instead of AMP(s).
 
Last edited by a moderator:
I used to wonder what a masochist was but now that I know I'm now left wondering if the masochist here is the OP for returning here to post yet again, or me for reading the post !!!
 
MATE in 12V or car speak, the abbreviation AMP to most people means AMPLIFIER, hence why I used the WORD "AMPAGE" instead of AMP, no auto electrician sayes "AMPERE" or "AMPERAGE", they say AMPAGE or AMP, but to car drivers, they would/may/might confuse this with car AMPLIFIERS. Hence they'd get confused about power watts and sound watts, hence the substituted full word AMPAGE, instead of AMP(s).

That's all well & good ............ or it would be IF this was a car forum, but it isn't !!!!
 
MATE in 12V or car speak, the abbreviation AMP to most people means AMPLIFIER, hence why I used the WORD "AMPAGE" instead of AMP, no auto electrician sayes "AMPERE" or "AMPERAGE", they say AMPAGE or AMP, but to car drivers, they would/may/might confuse this with car AMPLIFIERS. Hence they'd get confused about power watts and sound watts, hence the substituted full word AMPAGE, instead of AMP(s).

Unusually, this an explanation (to something that you posted) that can be described as reasonable ,even if not agreeable,so thanks for that
 
Here is the LONG version (After reading the 1st post SHORT version, thought I'd beef it up with some more data, details, etc):



PICTURE VERSION: WORD VERSION:
TOOLS NEEDS: MULTIMETER, SCREWDRIVERS & BLOCK CONNECTORS

This is quite simple see following pictures, the MultiMeter in this instance (DRAWN, POSITIVE TERMINAL) tests the AMPAGE between the POSITIVE SUPPLY (red probe lead) and the POSITIVE LOAD (black probe lead), this is known as breaking the circuit. Hence the NEGATIVE is uninterrupted from SUPPLY to LOAD (In other words, leave it alone). In this instance the positive supply has croc clips, normally I'd use insulated BLOCK CONNECTORS:

PIC1 (multimeter measuring AMPAGE between POSITIVE supply & POSITIVE load)


PIC2 (12V dc Battery Charger powering car cd player, with MultiMeter Testing AMPAGE)


PIC3 (CAR CD PLAYER in house install powered by CAR BATTERY CHARGER 12 V dc 4A)


PRECAUTIONARY NOTEs:
~ Obviously the NEGATIVE and POSITIVE can NOT touch each other (Neither SUPPLY or LOAD)
~ If your MultiMeter has NEGATIVE READING, your PROBE LEADS are the wrong way (Or ignore negative symbol, as AMPAGE figure is accurate).
~ The 12V dc MOTOR/PART or ALTERNATOR/SOLAR PANEL may CHARGE/DRAW a greater AMPAGE/CURRENT then the capacity of MULTIMETER & its LEADS (At this point the actual ampage is unknown). Eg: Most car electrical parts are low current (Indicators, elec windows, elec sunroof, heater, etc), with the obvious exception of a car starter motor (Extremely high ampage/current, totally unsuitable for testing with MultiMeter). Hence if 12V dc part/motor or charge rate of power supply is greater then 10A this may melt your MultiMeter probe leads and/or break the MultiMeter (Unless you have a 20A DC MultiMeter! Obviously the ampage max of those is 20A DC).

OTHER NOTES:
~ The AMPAGE reading of your MULTIMETER, is given by testing 'A' POSITIVE or 'A' NEGATIVE, however the AMPAGE reading is total AMPAGE drawn/charged, so this figure should NOT be doubled in your calculations.

~ My preferred practice/method, & the MOST accurate, is to connect new leads to the battery terminals, so there won't be any other registered ampage drawn from the car battery. So the ampage reading is what it is! (PS. Don't mess about from behind the car fusebox, keep it simple, either direct from car battery and loom OR new power leads from car battery to motor/part/device/appliance your testing with a MULTIMETER.)

~ Alternatively (The least preferred, & least accurate) If you're testing direct from a car battery and it's loom, it may have other parts/motors draining ampage, such as indicators/wipers, etc. So turn ON the ignition (WITHOUT STARTING THE CAR, as the ampage drain would be far too great for the MULTIMETER & PROBE LEADS!), then make a note of what the standard ampage drain is approximately (i), then turn on the motor/device/appliance you want to test (ii). Then subtract the standard ampage drain from the new figure with the appliance/device/motor on to EQUAL the difference (iii) i.e. The ampage of the motor/part etc.


FOR EXAMPLE:
i) STANDARD AMPAGE DRAIN = 0.5a (Car alarm or something else)
ii) STANDARD AMPAGE DRAIN & OTHER MOTOR = 1.5a
iii) CALC 1.5a - 0.5a = 1.0a

This guide is a quick reference when testing 12 Volt DC circuits with a MultiMeter, EITHER: ~ ampage CHARGE to batteries OR ~ ampage DRAWN from batteries.

Why test for AMPAGE? To determine what cable/lead thickness to use, and bigger is always better (Future proof, as you may add more devices to that circuit load). See rough guide below for 12v dc twisted wire (Not Socket wire):

CABLE SPECIFICATIONS for DC 12 Volts
THICKNESS (Either ~ Individual insulated wire thickness in mm APPROXIMATE)
AMPAGE (max of cable/lead/wire)
WATTAGE (max of cable/lead/wire)
2.7mm
3A
36w
3.0mm
10A
120w
3.8mm
20A
240w
5.0mm
35A
420w
6.2mm
50A
600w
1.2CM
AWG8 / 40A
480w
1.6CM
AWG4 / 70A
840w

To calculate correct CABLE/WIRE/LEAD thickness (Or FUSE Ampage) from appliance WATTS:
W = Watts, V = Voltage, A = Amps
W / V = A Eg 10Ws / 12v = 0.8A

Remember this isn’t exact, bigger is always better, thicker cable have less wear & tear overtime, & generally in 12v dc, thinner cable is also inadequate, because the motor/part/device can NOT draw sufficient current from thinner cable.
Here are some good examples, whenever I fit car sound amplifiers, OR large inverters into cars I use AWG8 which has an ampage of 40A, which is far greater ampage then the car sound amplifier or inverters, such as:
~ 40A / 4A (Ampage of an large inverter) = cable 10 times the ampage of the inverter
~ 40A / 20A (Ampage of a 4 channel 400 Watt car sound amplifier) = cable 2 times the ampage of the inverter
Hence fitting much larger ampage cable, then the actual ampage of the device (car sound amplifier or inverter) is common good practice.
To calculate power WATTS max for circuit (If the rest of your system is specified in 12V Watts rather then 12V Ampage):
W = Watts, V = Voltage, A = Amps
A x V = W Eg 20A x 12V = 240Ws (Power Watt’s NOT sound Watt’s)

TYPICALLY AMPAGES OF MOTORS/PARTS/DEVICES:
AMPAGE (12V dc) rated P/H given as multimeter instant reading
PART
1A to 1.6A (Depends on music played!)
CD/MP3 PLAYER
3A to 20A+ (Depends on the music being played!)
car sound AMPLIFIER 400 Watts 4 Ch
0.01 A
CAR CD PLAYER AMPLIFIER REMOTE
0.03 A
4 WAY CIG LED MULTI ADAPTOR
0.60A (Maximum 0.70A)
PORTABLE DVD PLAYER
2.3 A
CAR INVERTER CAN
5.3A to 6A = Charging Laptop
(inverter on = 0.4A, inverter off = 0A)
CAR 12V to 240V 1000 Watt Inverter
0.28 a
MOBILE PHONE CHARGER
0.05 A
SATELLITE NAVIGATION
0.06 A
BLUTOOTH CHARGER
2.6 A est
FLASK
4.6 A
PUMP
0.20A (Depends on function)
LED LIGHT
12.00A
HEADLIGHTS
0.03A
ALARM DRAIN
3.00A
ALARM CENTRAL LOCKING
0.36A
INTERIOR LIGHT
0.08A to 0.20A
ALARM/IMMOBILISER
6A
HAZARD LIGHTS
8A Each
ELEC WINDOWS
10A +
ELEC SUNROOF

IMPORTANT NOTE: Cable size, the bigger the better (Bigger: Diameter or circumference of the cable).

Remember most MultiMeters (£10 Maplin job ok) only test upto 10A 12V DC, more expensive MultiMeters (UNI-T from Maplin £30 why spend any more) test upto 20A 12V DC.
 

Attachments

  • AmpageTesting12VoltDC.jpg
    156.9 KB · Views: 13
Last edited by a moderator:
Also remember when you are FITTING (Instead of just testing) power cable, remember the circuit should be adequately fused, for example from SUPPLY (Battery Terminal to Fuse, via ring connector to cable) to the LOAD (Cable, then Motor/Device). Remember the fuse rating is lower then that of the cable ampage, hence if the current is greater then the fuse ampage, the fuse will blow, and if the power negative & power positive touch uninsulated then the fuse will blow because of resistance (The touching of opposites, - and +). Remember a fuse is only a fuse (Cheap & easy to replace), how if you don’t fuse a lead, and resistance and/or maximum is exceeded, then wiring looms and/or motors/parts and expensive & hard to replace (Certainly NOT cheap & easy to replace). Hence on my car I have fused separately the positive & negative, for extra security, as I said before a fuse is only a fuse, to replace fuses, are cheap & easy.

306CarBattery2.JPG
CABLE & FUSE example for 2 typical 12 Volt dc devices

INVERTER
car sound AMPLIFIER
CABLE
40 A
40 A
FUSE
10 A
30 A
DEVICE (Eg Inverter or Car snd AMP)
4 A
20 A

To calculate power WATTS max for circuit (If the rest of your system is specified in 12V Watts rather then 12V Ampage):
W = Watts, V = Voltage, A = Amps
A x V = W Eg 20A x 12V = 240Ws (Power Watt’s NOT sound Watt’s)


TYPICALLY AMPAGES OF MOTORS/PARTS/DEVICES:

PART
AMPAGE (12V dc) rated P/H given as multimeter instant reading
CD/MP3 PLAYER
1A to 1.6A (Depends on music played!)
car sound AMPLIFIER 400 Watts 4 Ch, 2 channels bridged powering SUB & 2 channels for 2 6x9’s
3A to 20A+ (Depends on the music being played! Eg about 20A @ Vol 25)
CAR CD PLAYER AMPLIFIER REMOTE
0.01 A (Constant when amp used)
4 WAY CIG LED MULTI ADAPTOR
0.03 A
PORTABLE DVD PLAYER
0.60A (Maximum 0.70A)
CAR INVERTER CAN
2.3 A
CAR 12V to 240V 1000 Watt Inverter
5.3A to 6A = Charging Laptop
(inverter on = 0.4A, inverter off = 0A)
MOBILE PHONE CHARGER
0.28 a
SATELLITE NAVIGATION
0.05 A
BLUTOOTH CHARGER (Nokia)
0.06 A
FLASK with optional warmer
2.6 A est
PUMP 12V
4.6 A
LED GRILL LIGHT IN RED
0.20A (Depends on function)
HEADLIGHTS
12.00A
ALARM DRAIN
0.03A
ALARM CENTRAL LOCKING
3.00A
INTERIOR LIGHT
0.36A
ALARM/IMMOBILISER
0.08A to 0.20A
HAZARD LIGHTS
6A
ELEC WINDOWS
8A Each
ELEC SUNROOF
10A +

IMPORTANT NOTE: Cable size, the bigger the better (Bigger: Diameter or circumference of the cable).

Remember most MultiMeters (£10 Maplin job ok) only test upto 10A 12V DC, more expensive MultiMeters (UNI-T from Maplin £30 why spend any more) test upto 20A 12V DC.

ALTERNATIVELY To test AMPAGE of 240 VOLT ac APPLIANCES use a plug in ENERGY MONITOR (From Maplin).
 
Last edited by a moderator:
now i know what current my windows require, i shall sleep better at nights. however in the morning, i'll still have to use the window winder handle as they're not electric. now i'm just off to the "manual van window forum"
 
What was the point in that post? Most multi meters only test to 10amps so for anything more they're useless. All you need is an amp clamp multi meter, good for 600amps, or an inductive ammeter they cost pence. But in this technological world you can buy a digital ammeter with fuse adapter on the end for five quid. A lot easy than than mess in the pictures! Stick to stealing car stereos!
 
What was the point in that post? Most multi meters only test to 10amps so for anything more they're useless. All you need is an amp clamp multi meter, good for 600amps, or an inductive ammeter they cost pence. But in this technological world you can buy a digital ammeter with fuse adapter on the end for five quid. A lot easy than than mess in the pictures! Stick to stealing car stereos!

Mate, In the 12V dc car/house world nearly every part/motor with the exception of a car starter motor, is less then 10A, the only other common exceptions being high output car sound amplifiers, perhaps some air conditioning units, so a 10A MultiMeter £10 or 20A MultiMeter £30 is more then adequate.

Clamp MultiMeters and PAT testers are useless junk, they are a joke, they're expensive mickey mouse nonsense(Metal conducts, but NOT wirelessly!)

And the other meters, are a waste of time & money (Make a circuit, wait an hour, or average out 10 mins over an hour). I guess your making reference to finding out the ampage of a starter motor, goto Halfords (Or your main dealer) and ask them the part (starter motor) specification, it sayes on the side of the box.
 
Last edited by a moderator:
Mate, In the 12V dc car/house world nearly every part/motor with the exception of a car starter motor, is less then 10A, the only other common exceptions being high output car sound amplifiers, perhaps some air conditioning units, so a 10A MultiMeter £10 or 20A MultiMeter £30 is more then adequate.

Clamp MultiMeters and PAT testers are useless junk, they are a joke, they're expensive mickey mouse nonsense(Metal conducts, but NOT wirelessly!)

And the other meters, are a waste of time & money (Make a circuit, wait an hour, or average out 10 mins over an hour). I guess your making reference to finding out the ampage of a starter motor, goto Halfords (Or your main dealer) and ask them the part (starter motor) specification, it sayes on the side of the box.

interesting thread srands,it inspired me to have a bit of a tinker with my own car,tho i think ive bit off more than i can chew...look forward to your help..:uhoh2:


full car in bits pic.jpg
 
Remember a fuse is only a fuse (Cheap & easy to replace), how if you don’t fuse a lead, and resistance and/or maximum is exceeded, then wiring looms and/or motors/parts and expensive & hard to replace


Why would you want to fuse the negative as well as the positive
A circuit will be disrupted with a fuse in the positive only,adding another fuse in the negative has no benefit,its a waste of time and effort


Some starter motors can draw current upwards to 200 amp and will operate directly from the battery via the solenoid,
If you double fuse everything ,does that "everything" include your starter motor

Using thick cables to overengineer for heavy future loads
Relays and solenoids negate the need to switch the bulk of these loads,localised larger cable is the time tested best method
 
To comment further on calculating AMPAGE drawn, there was discussion that electric motors are all mostly low ampage (Below 10Ah), with the exception about knowing the ampage of a car's greatest electrical consumption part, a STARTER MOTOR, well goto Starter Motor | Quality Starter Motors for any car (Or your main dealer) and ask them for the parts (starter motor) specification, it sayes on the side of the box, or motor.
Note: If starter motor specification is in KW:
KW / 1000 = Watt's
Watt's / 12 V = A. This figure is an instant, as the starter motor drain is for a second (NOT continuously), then the ignition key is released (Starter motor turned OFF) as the engine is started, then the alternator produces current, recharging the battery, obviously there will be small current drains in Ah from small motors/parts, for example, electric windows, indicators, car cd/mp4/dvd player, lights, fan/air con, etc.

FURTHER DETAIL:

BATTERY & STARTER MOTOR EXAMPLE:
CAR BATTERY: 56 Ah (* 10 = 560 A [EN])
STARTER MOTOR 1.7 KW (/1000 = 1700 WATTs / 12 VOLTs = 142 A [EN])

Obviously the car manufacturer deems what is an appropriate battery Ah for their manufactured car model.

An Amp-Hour (ampere-hour, Ah) is a way of describing a battery's capacity - how long it will run before it is drained down. To be more specific: the amp-hour rating for a given battery is the maximum amperage that can be drawn continuously until the battery is completely flat, over a specific time period.

AH stands for amp hours
10 amp hours =
~ DrAW 10 amps for 1 hour
or
~ Draw 1 amp for 10 hours
Or
~ Draw 11 amps for 54 minutes (0.9 hours)
The faster you draw amps out of your battery the fewer amp hours you get in total, and the shorter the life of the battery.

Ampere-hour - Wikipedia, the free encyclopedia
Starter Motor | Quality Starter Motors for any car
 
Last edited by a moderator:
Thanks for link to Ampere-hours, you learn something everyday!
Could you please explain to me kWh, I'm just completely baffled by them?
Thanks in advance
A
 
Thanks for link to Ampere-hours, you learn something everyday!
Could you please explain to me kWh, I'm just completely baffled by them?
Thanks in advance
A

This needs explaining from both 12 Volt DC and 240 AC Volt perspective:

12 Volt dc, we're NOT concerned about the cost of electric, because a car alternator generates this for free (Well apart from fuel & wear & tear of car & driver!) as is a by product of engine running (One cog turns, a belt to the alternator, another cog turns, electric produced, power lead to battery, charging battery). Hence the only real preoccupation here is what is the AMPAGE of the PART (If unknown use MultiMeter to determine, see 1st msg in this post)? Once this is known, then specifying the correct THICKNESS LEAD/CABLE and FUSE is one of the only fitment considerations

Calcs (W = Watts, V = Voltage, A = Amps):

1000 W's = 1 KW (In other words W * 1000 = KW)

A x V = W (Eg 0.8A * 12v = 10Ws)

W / V = A (Eg 10Ws / 12v = 0.8A)

Ah x 10 = A (EN) (Eg 56 Ah * 10 = 560 A [EN])

DC 12 Volt Cable Guide
Individual insulated wire thickness in mm with approx max
AMPs
WATTs
2.7mm
3A
36w
3.0mm
10A
120w
3.8mm
20A
240w
5.0mm
35A
420w
6.2mm
50A
600w
1.2CM
AWG8 / 40A
480w
1.6CM
AWG4 / 70A
840w



Note: To power an AC 240 Volt appliance in a car, you need an INVERTER (I'd recommend a very generous maximum margin to power your SMALL appliance, such as I have fitted 1000W Inverter for a 100W LAPTOP!). WHY? Because your laptop voltage is different to your car battery, for example: Car batteries = 12V. My Laptop power = 20V with psu (Power Supply Unit AC to DC). And bigger is always better, as may use USB powered extras (Hard drive, cameras, etc), or may get larger spec laptop.

240 Volt ac, we ARE concerned about the cost of electric, because ELEC is charged by the KW.
Small Appliances are stated in WATTs (This figure is the approx figure IF an appliance is used for AN HOUR, even though the reading on ENERGY MONITORS is instantly displayed. For example a kettle may only be used for 3 mins, and it's max maybe 2200 Watt's, however it's consumption is NOT 2200 Watt's unless it is used continuously for an hour!).
Large Appliances over 1000 Watt's are stated in KiloWatts such as KETTLES, DISH WASHERS, WASHING MACHINES, etc.
ELECTRIC used in houses/businesses is measured with an ELECTRIC METER, and in KWs.
Once again specifying the correct THICKNESS LEAD/CABLE and FUSE is an important fitment consideration. Since appliances already come with a LEAD, the same thickness or bigger is adequate. The FUSE must be greater then the Ampage max of the appliance and the cable lead must be thicker Ampage then the fuse Ampage.
However if fitting new SOCKET RING/RADIAL circuit need to be fitted, consideration has to be given the total max in amps of all applainces using that circuit, hence use appropriate socket wire cable, sockets/fixtures, etc.

AC 240V (Appliance Wire) Cable Guide
Individual insulated wire thickness in mm with approx max
AMPs
WATTs
0.2mm
1A
240w
0.5mm
3A
720w
0.75mmm
6A
1440w
1.00mm
10A
2400w
1.25mm
13A
3120w
1.5mm
15A
3600w
2.5mm
20A
4500w
4.00mm
30A
7200w

AC 240 Volts (Socket/W) Cable Guide
Individual insulated skt wire thickness in mm with approx max
AMPs
WATTs
1mm
15A
3600w
1.5mm
20A
4800w
2.5mm
27A
6480w
4mm
36A
8640w
6mm
46A
11040w
10mm
63A
15120w
16mm
85A
20400w


Want a FUSEBOX CIRCUIT and MCB/RCD calculator? See my spreadsheet MCB/RCD CALC See the 3rd tab (If MCB's are different ampages) or 4rd tab (If MCB's are same ampage)


Calcs (W = Watts, V = Voltage, A = Amps):

1000 W's = 1 KW (In other words W * 1000 = KW)

A x V = W (Eg 5A * 240v = 1200Ws)

W / V = A (Eg 1200Ws / 240v = 5A)

Note: To power a DC 12 Volt appliance in a house, you need either an adequate:
~ AC to DC plug: Maplin stores, Mobile phone stores, or stalls in retail shopping centres)
or
~ AC to DC psu (power supply unit): Maplin stores
or
~ CAR BATTERY

Still need more ELEC/utility calculators?
See my very comprehensive workbook spreadsheet (See 1st tab, scroll down) ELEC GAS WATER autocalc: 1st tab, scroll down
 
Last edited by a moderator:

Reply to AMPAGE TESTING (12 Volt DC) in the Australia area at ElectriciansForums.net

Similar Threads

I have a loading arm on a vehicle powered by a hydraulic motor powered by a 12 volt motor. The motor is initiated by proximity switches on the...
Replies
0
Views
791
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
Im trying to make a Star Wars Prop for a course project where the dealine is comming up very fast in days and I need to do the report so really...
Replies
0
Views
395
I want to operate 3 lighting set up using metal halide lamps for studio works or cinematic projects in the future. as of now i have got two...
Replies
0
Views
1K
I bought a used golf cart a few days ago which had their batteries replaced last year. They hooked up an am/fm radio to it and it worked fine when...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock