The DNO supply comes into the green cabinet, and within this cabinet there is a 4w 3ph dist board.
The 4c 25mm SWA runs from here to the garage, to another 3ph dist board, then from here to the house.
There is a duct from cabinet to garage, so an additional bond could be pulled in, but as I say, the incoming water is plastic.
My worry is : if the DNO supplies the means of earthing (TNCS) and their cutout and fuse is in the green box at the boundary, then the installation's MET should be there. So if you are using SWA armour from green box to garage then it's insufficient for bonding to the garage too.
 
My worry is : if the DNO supplies the means of earthing (TNCS) and their cutout and fuse is in the green box at the boundary, then the installation's MET should be there. So if you are using SWA armour from green box to garage then it's insufficient for bonding to the garage too.
Thanks, but if the incoming water is plastic, there is no gas/oil, RSJ's are enclosed, and there is no other exposed metal work, what do you bond to?
Like I said, it would be possible to pull a 10mm in (using the SWA as cpc).
So providing there is no bonding requirements, using the PME earth is ok.
 
I don't know the specifics, please tell me somebody.

If you have an extraneous conductive part, is it relevant wether it's exposed or not? I would have thought you would have bond it regardless. I certainly would personally.
 
I don't know the specifics, please tell me somebody.

If you have an extraneous conductive part, is it relevant wether it's exposed or not? I would have thought you would have bond it regardless. I certainly would personally.
The garage and house are timber framed, with the rsj in the house resting on timber supports, so not going to have a potential to earth.
 
My feelings for what they are worth are, pull in another CPC from the incomer position to the garage then onto the house, terminating at each point in a single way service block. This means you have covered all bases, you know what they say assumption is the mother of all ****up's.
 
Can you 100% guarantee the metal work is enclosed throughout and will remain enclosed?
It would difficult to achieve if the metalwork was extraneous, you often see it partially boxed in for aesthetic purposes or given fire protection but as you say to totally contain it 100% would be all but impossible especially on large structures and not cost effective, you may as well bond it. From what the op says it doesn't sound extraneous.
 

Reply to Another "exporting PME post"... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
430
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
HI all, customers are building a small house and im coming off thier PME supply to the new build, 25mm 3 core SWA, small two bed house about...
Replies
10
Views
2K
Hi everyone, I have a quick question if I may? I'm thinking of adding a second PV system to my existing rooftop PV & battery setup. As the...
Replies
0
Views
1K
Hi ok here we go. Friend has asked if can rewire his garage as he is turning it into a gym. I said ok no problem. He the put the spanner in. Ok...
Replies
50
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock