Discuss Any thoughts on this old thing? in the UK Electrical Forum area at ElectriciansForums.net

timhoward

-
Esteemed
Arms
Supporter
Reaction score
8,907
Quite old main switch RCD, it occasionally trips (every day or two), then won't turn on until all breakers are off.
Ramp test at time of testing was 25ma, earth leakage meter said 5ma (so consistent).
Is the RCD likely to simply be old?! Are they tetchy switching on under load?

Haven't got into IR testing yet. Their initial enquiry was for a CU change so a DP RCBO board will likely solve all issues or worst case show up anything that has intermittent faults.

1690485637044.png

1690485674025.png
 
. I have an ex council estate near me where most of the houses seem to have those mem boards with the funny handle RCD. i have had a few times when doing an EICR done my trip time test on the RCD and the RCD trips and literally breaks and the switch just goes floppy. its was a good job I live locally and used to keep a small inventory of boards in my garage to do a quick emergency board change.
 
OP's RCD tripping immediately when switched on with RCDs on is probably the residual leakage plus a capacitive surge as all the wiring 'charges up', plus possibly a bit of E -N leakage somewhere causing a pulse.
The 'floppy handle' is the mechanism that stops the RCD being held on against a fault sticking in the disconnected state. Usually caused by failure t regularly test the RCD with the button, and normally cured by a bit of 'exercising' of the mechanism.
In a couple of decades time, I'd trust a 50 year old RCD labelled made in West Germany against a 20 year old one labelled made in PRC.
 
Thanks Brian.
They have decided to change it to a double pole all-RCBO Fusebox effort. As one of them works from home the nuisance tripping is quite an erm... nuisance.
I'm hoping that the process of the board change (IR testing etc) will reveal some likely candidates for the issues, that the division of the leakage will improve matters, and in worst case one circuit will trip. We'll see!
 
I was called out to a nuisance RCD tripping, yesterday, not one of those but a wylex one.
Did some tests and the ramp told me it was tripping at 21ma.
Turned the circuits back on 1 by 1 with a clamp on the main tails and watched the leakage reach 19ma!
The place was absolutely full of tec, chargers plugged into multi gang adaptors, half of them unused it turned out.
Got the final reading down to 12ma by the time the client and I had been round every room.
Got to quote for a full RCBO board for that job, 4 socket circuits, cooker, shower, immersion and outside man cave all on one 63a RCD!
 
Now changed the board. Two 0.0x IR readings, one traced to outside light, the other on upstairs sockets which soared when a highly mangled iPhone charging cable was removed from a USB socket.

It's the first time I've changed one of these, and I rather liked the old board....it felt well made.
I appreciated the effort the original installer went to:

1690983928804.png


Only one complaint - can anyone spot it?

And in with the new:
1690984254074.png


(Let's see if a conscious decision I took attracts anyone's attention!)
 
Two 0.0x IR readings, one traced to outside light, the other on upstairs sockets which soared when a highly mangled iPhone charging cable was removed from a USB socket.
The charger must be broken then if it has primary (mains) to output (USB) lead continuity!?

Maybe I'm odd (OK, yes I am odd) but when PAT testing the likes of USB chargers, PoE injectors, etc, I treat "class II" testing with the earth clamped to a butchered USB/network cable so I can check for insulation failure inside. Thankfully not found a dangerous one yet, but you do read of the occasional death from that (often involving eBay fakes and a bath as well).
 
That’s not the right bus bar shield, surely??
Its covering up half of the yellow rcbo test button
It actually is the right shield, I just didn't fit it correctly before taking the photo. It's fine now (honest!)
Maybe my eyes are deceiving me, but is it a cut-off CPC on the incoming T&E?
Yes, that was the main thing. There's a separate 10mm CPC but I didn't like the T&E being un-earthed. I didn't want risk damaging the rather short incoming T&E so I earthed it the other end (also cut off) and there's now a wago on this end and a notional 4mm to the CPC bar.
The charger must be broken then if it has primary (mains) to output (USB) lead continuity!?
Yes, it was actually a plug in apple charger not a USB socket, my mind wandered!
The apple charge plugs are earthed, and I was getting a N+E fault show up. I binned the lot, but in hindsight some more tests would have been quite interesting, as it suggests a primary/secondary link/fault on one side of the coil.

The more minor thing that some would say is wrong with my install hasn't been spotted yet. It's related to an area of scrutiny that Westy specialises in....
 
I didn't know Westy specialised in the lack of grommet strips.
Fair! I was expecting some in the brown envelope and they were missing. I decided as the wall opening was higher than the lower edge I wouldn't lose too much sleep over it.

That still wasn't the thing I was thinking of though! It will be interesting to see how many more things I've done....!
It's something the original installer also did.
 
Polarity reversed at incoming tails?
Good God man you know how to make someone's heart skip a beat!
No, we both got that right!
(One of my biggest concerns was the length of the main N but it worked out ok, just!)

No, it's a very minor thing, as we all tend to be a pedantic bunch I was expecting someone to slap me for it straight away.
It would probably first be noticed if you had to test certain circuits.
 
Good God man you know how to make someone's heart skip a beat!
No, we both got that right!
(One of my biggest concerns was the length of the main N but it worked out ok, just!)

No, it's a very minor thing, as we all tend to be a pedantic bunch I was expecting someone to slap me for it straight away.
It would probably first be noticed if you had to test certain circuits.

Not familiar with that old incomer and didn't want to assume busbar connection to it, but lettering appeared to show 'L' above left terminal.
 
Bonding in the right hand earth terminals meaning every cicruit is shuffled to the left
Ah they were a little short... and there are some spare terminals.
I didn't know Westy was a stickler for sharing earth sleeving with multiple conductors.
That's the one I was thinking of. And maybe he isn't, maybe it's just sleeving size?!

The original had the CPC's twisted together impressively tightly to the degree I didn't want to risk unwinding them.
So did testing at a socket and left them well alone.
 
If the cores are really short but just about reach one side of the bar then i will always do what you have done and just shuffle everything down / up to avoid jointing cables.

Likewise if the cores are alrteady twisted within an inch of their life it is often better to leave alone than risk unwinding them just to have it snap right at the top of the cable.

Don't teach stuff like this in the class room
 
the sharpie marks on the ring finals weren't necessary, don't like sharpie marks.
I'm always happy to learn new tricks. What do others do? Mark cable sheaths where visible? Cable marker clips? Trust you keep them in same order?
My old gaffer used to put nicks in the cables which I never liked!

The number of times I find one leg of a ring swapped with an immersion heater has left with me no qualms about leaving future electricians clues! But I'm open to better ways.
 
I'm a shameless Sharpie charlatan. But I agree it looks ugly. I have used tape 'flags' and marked the tape with a Sharpie, but they are prone to coming off the cables when the old fuse box is removed.
 
Hate when peoplle nick the cable , some older sparks I worked with did this and to me was just rough house...

a white tape flag and write on on in biro when doing board swaps was probably me go to, or a little dyno lable
 
I'm always happy to learn new tricks. What do others do? Mark cable sheaths where visible? Cable marker clips? Trust you keep them in same order?
My old gaffer used to put nicks in the cables which I never liked!

The number of times I find one leg of a ring swapped with an immersion heater has left with me no qualms about leaving future electricians clues! But I'm open to better ways.
Three rings, cut the ends off one, leave one as it was and strip longer ends on the other.
 
I'm always happy to learn new tricks. What do others do? Mark cable sheaths where visible? Cable marker clips? Trust you keep them in same order?
My old gaffer used to put nicks in the cables which I never liked!

The number of times I find one leg of a ring swapped with an immersion heater has left with me no qualms about leaving future electricians clues! But I'm open to better ways.
If all the rings tested out before the board swap then it's just a case of a quick continuity test to put the rings back together. No sharpies or flags required.

They're tests you have to do anyway.
 
Not sure about that 3 - 1- 2 on the RFCs :)
What's that all about?
The marks were put on before I dismantled the old board, before I proved end to end continuity and before I proved there were no inter-connections. I do this if it’s a shared RCD or no RCD as a record of how it was installed.
Just a little insurance policy really.

I’ve had a house once where some highly creative smoke alarm wiring was linking most circuits together. Live from light switch, N from nearest socket etc, and the immersion and the kitchen ring were also involved as well as a link back to a lighting circuit at the CU.
After that rather horrendous diagnostic experience I tend to mark the original position of the 2.5’s.
 

Reply to Any thoughts on this old thing? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
2K
I will start with apologies, as I have not thought this through very much (at all) yet and have just sat down with a beer.... meaning I thought...
Replies
3
Views
1K
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock