I think that termination technique is at least as important as torque.

For example, I have been in the habit of 'untwisting' the strands of some larger cables (tails) when terminating as I reasoned that the strands could then move freely to take up a minimum space in the terminal and be less prone to loosening.

There was a report about this a couple of years ago:
http://www.electricalsafetyfirst.org.uk/mediafile/100015987/Switched-On-24.pdf
See pages 14 and 15.

The original experimental report is here:
http://www.electricalsafetyfirst.org.uk/mediafile/100013801/Meter-Tail-Investigation-Report.pdf

I think that untwisting rather than 'flattening' is what matters. The group of strands will take up the shape of the terminal when tightened.

The technique is probably not of any use for small cables with fine strands in some large direct screw terminals, as the strands will just displace up the sides of the screw.
 
I think that termination technique is at least as important as torque.

For example, I have been in the habit of 'untwisting' the strands of some larger cables (tails) when terminating as I reasoned that the strands could then move freely to take up a minimum space in the terminal and be less prone to loosening.

There was a report about this a couple of years ago:
http://www.electricalsafetyfirst.org.uk/mediafile/100015987/Switched-On-24.pdf
See pages 14 and 15.

The original experimental report is here:
http://www.electricalsafetyfirst.org.uk/mediafile/100013801/Meter-Tail-Investigation-Report.pdf

I think that untwisting rather than 'flattening' is what matters. The group of strands will take up the shape of the terminal when tightened.

The technique is probably not of any use for small cables with fine strands in some large direct screw terminals, as the strands will just displace up the sides of the screw.
to be fair on tri-rated etc we would just use ferrules.

personally i would always use ferrules on stranded unless its a cage clamp type termination
 
Unless torquing to a high setting with a T-bar or similar or torquing to a low level to prevent shearing I find little use for a torque screwdriver. I've always found torqueing to 'hand tight' to be pretty useless as this is easily judged by feel.
 
I have that one. Personally I don't go with the settings that the manufacturers say because for example if you tighten a screw up on the earth or neutral bar, say it's on 1.0mm cable then it just breaks the conductor so how are you supposed to do it eh. I personally think you are better using your own judgement, like I say if you do as per the manufacturers instructions it with break the conductors.
 
Work issued me one and it's handy to have. It saves you wrenching the mcbs and causing them damage and it also saves fatigue on your hands by needlessly over tightening. The kits really good and easy to setup. Just watch 1mm connection as they might snap due to torque setting.
 

Reply to Anyone got Wiha Torque screwdriver in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi Chaps I've got a Wiha torque driver but only came with couple of bits (below)... none of which fit 'outgoing side' of Contactum RCBO's...
Replies
13
Views
1K
Well i brought a set because i needed this MOD1 &2 (wouldnt mind but the shops didnt even know what i was talking about) S1&PH !! well ANYway i...
Replies
13
Views
585
Long time no see and I hope you're all doing well. I see that torque screwdrivers have become the height of fashion in the UK over the last...
Replies
96
Views
10K
I was working alongside the plumber yesterday. I had to drill some 32mm holes through joists. I always use my Makita 481 high torque drill will a...
Replies
29
Views
2K
I have had mine about 3 years ( maybe longer ) and have never bothered to have it reset Does anyone or has anyone bothered to have their vde...
Replies
9
Views
2K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock