Discuss Arcing contact problems and voltage measurements - some thoughts in the UK Electrical Forum area at ElectriciansForums.net

Some good points there Alasdair. The likely inaccuracy of measurement of non-sinusoidal voltage should have been raised at the time, but I think we got bogged down trying to work out whether the drop referred to was in the switch or the supply cable. In any case we never even found out what instrument took the measurements. It's still not clear to me how any significant drop could have occurred in the switch as the mean dissipation could not have been more than a few dozen watts without visible signs of overheating. The damage within the case loooked more like the result of brief, intense arcing, such as when closed onto a short.

To put this to bed, I would like to do a practical test of the sensitivity of an MCB to extreme waveforms, e.g. by playing an arbitrary waveform generator through a laboratory amplifier and transforming down to get a test supply of up to say 100A pk. My hunch is that the MCB will stay in spec for thermal tripping accuracy wrt. RMS current, but the magnetic trip could do anything. I might try this if the Christmas celebrations start to drag on too long. However, since there was a resistive load (we think) in series at all times, we were generally in agreement that the magnetic trip was never involved.

The bottom line is that although we know how the fault was cured, we don't truly know the nature of the fault itself.
 
TESTS.... of the sensitivity of an MCB to extreme waveforms, e.g. by playing an arbitrary waveform generator through a laboratory amplifier and transforming down to get a test supply of up to say 100A pk. ...The magnetic trip could do anything. I might try this if the Christmas celebrations start to drag on too long..
Have wondered if arc may have fluctuating DC componenets that may be occasianally reversing . If the intermitency - hits natural resonance
with occasional impulses .(Sods law and when you want random symetry ... a DC componenet may desensitize ... magnetize ..then reverse (expecting resonances to change with manufacturer geometry)
-- Keep up the up the LAB work Lucien --
....... in extreme cases heating of the skin.
We were warned eye corneas have little blood flow to remove heat ..
(remembered watching my dinner in the microwave -- cyclic pattern)
 
Last edited:

Reply to Arcing contact problems and voltage measurements - some thoughts in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
M
Hi all, I live in a block of flats with communal garages and have been tasked with resolving a minor electrical issue we may have. (Having no...
Replies
8
Views
2K
Mark Bat
M
P
Hi guys, I have no idea if this makes any sense, but I’ll give it ago with the hope of getting a better understanding. I know that a capacitor is...
Replies
2
Views
2K
My customer read on many forums about people suffering to solve a problem with the above Land Rover with regards to a fault code known as P1260...
Replies
5
Views
29K
J
Hi folks Iknow this topic has been beaten to death on this forum but after reading some of the posts and speaking to some of my co workers I am...
Replies
3
Views
3K
johnohagan
J

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock