Discuss Arcing on gas bond in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

J

jmtisme

Hi got a problem with a PIR I am doing got small arcing when putting bond on to main gas pipe getting .5v when measured across pipe and bond had gas board out they proved that incoming pipe is in plastic disconnected all earths and still getting it discon earths and neutrals still getting it.
 
You are testing between gaspipe to earth while bonding is not connected to pipe i assume to see what voltage difference there is present, although 0.5v isnt very large there could be a large current flowing, have you clamp tested the bonding to gas to see if curent is flowing, also switching off full mains and retesting will confirm if source of voltage is from installation to premises.
 
Have clamp tested the main earth bond going into consumer unit there was nothing on it will test the bond now all my tests on this were with main fuse pulled thanks again :)
 
An arcing on a bonding condutor could be a a sign of a fault. What system have you got there is it a TNC-S or TT?

You can sometimes get a fault from another property that will track back to your bonding through the TNC_S PME or the TT rod. You say the gas board have confirmed the pipe is plastic, is the water also plastic?

As Darkwood says I would completely isoalte your installation either from the double pole isolator switch, that way you know if your installation is cauisng the problem
 
I have isolated the supply and removed bond from water pipe it still arcs. The fault can not be on the installation of the property I am working on. Any more help would be great thanks again guys.
 
Isolate all of the earths individually and see if you have any additional (possibly redundant bonds) and see where the induced voltage is comming from. The gas may be source, or it could be the exit path to earth. What does the gas supply?? is it a shared supply, any external circuits e.g. out buildings with connected spike. This is a difficult one to diagnose remotely and all you will get is plenty of well educated guesses and possibly if you are lucky solutions....

If the gas supply is confirmed as being plastic (no path to earth and internal is copper), then there must be a fault on the equipment it supplies.
 
Thanks again guys will check today if the gas supply is shared. Should I leave the bond disconnected or would it be safer to have it connected thus grounding any possible fault
 
Gas service is not shared but water will be shared through copper and this goes through a boiler which is connected to the gas.
 

Reply to Arcing on gas bond in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
876
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
798
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock