Hi,

I had a nice little job of cutting 20 Australian plugs off appliances etc the other day and replacing with uk plugs...

It occurred to me though, none of them had fuses?..

I have no idea how it works down under and just wondered if someone would kindly tell me why the appliances are not fused.
 
Ring final circuits and fused plugs are an entirely british thing and only appear in this country and some of those we used to own.

Everywhere else they use radials and the protection for the appliance flex is provided by the OCPD

Don't forget the plug fuse is only intended to protect the appliance flex as the 32A OCPD is too big for the purpose.

We do also use unfused plugs in the form of everthing other than the 13A plug. You don't find fuses in 10A IEC plugs, 16, 32, 63 or 125A plugs or 400A powerlock plugs
 
Multiple radial rcd protected socket circuits fed from 10 amp fuses - that's how they do it.

Our British 32amp ring circuits are not common outside the UK thankfully, but let's not open this thread up to a ring vs radial argument again!
 
Depends how many outlets said radial feeds and where they are...don't personally fancy crawling through the founds and coming across a redback /black widow /taipan best. ...
Weather would be a boon though
 
Depends how many outlets said radial feeds and where they are...don't personally fancy crawling through the founds and coming across a redback /black widow /taipan best. ...
Weather would be a boon though

Here in Victoria it's the bloody tiger and brown snakes you look out for and those tiny nipping ants that get everywhere!!
 
Malta, Hong Kong, India and Eire are hardly surprising!


India and Pakistan NO, (well not that common anyway) they still use the old BS 15A and 5A outlets. But most of the Middle East especially in the Emirates, you'll find them in use on prestige buildings, Malaysia, Singapore, Cyprus, as well as a good few more. Also the two projects i've worked on here in China are using the BS 13A outlets and ring circuits. They also use the old BS15A outlets for bigger load appliances like AC's etc.... Though the most common outlet system over here is the Ozzi outlets and the multi system outlets, neither of which i rate very highly!!
 
It is a pet hate of mine to hear people refer to BS546 connectors as being old or obsolete etc!
They are alive and well in the entertainment industry, all small dimmer circuits (2.4KW) in nearly every theatre is connected via 15A plugs and sockets.

I believe they are used in South Africa too but with a 16A rating
 
5A and 15A BS546 are great for dedicated supplies to fixed appliances. The 2A sockets ideal to be added to a lighting circuit.

They ain’t dead yet.
 
It is a pet hate of mine to hear people refer to BS546 connectors as being old or obsolete etc!
They are alive and well in the entertainment industry, all small dimmer circuits (2.4KW) in nearly every theatre is connected via 15A plugs and sockets.

I believe they are used in South Africa too but with a 16A rating

I didn't say obsolete, but they are an older design and are now basically relegated to specialised installations such as in theatres and the like in the UK.

Yes they are very popular still overseas, and are often used in 16A/20A dedicated circuits. One things for sure, they are more than capable of carrying a lot more than there 15A rating!! You only have to physically compare them to a flat pin US 20A plug top to see that... lol!!
 
It is a pet hate of mine to hear people refer to BS546 connectors as being old or obsolete etc!
They are alive and well in the entertainment industry, all small dimmer circuits (2.4KW) in nearly every theatre is connected via 15A plugs and sockets.

I believe they are used in South Africa too but with a 16A rating
Yep, we class them as 16A plugs and they're standard for appliances. Final domestic/light commercial circuits are all 20A radials on 2.5 flat twin (or separate wires in tube) with 4 sockets per circuit. We generally use c curve ocpd's for socket circuits. I don't see a problem with having an unfused plug on a 20A circuit as long as trailing leads/appliance cords are of a decent CSA size and not above a meter or two in length.
 

Reply to Australian Plugs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A friend of the family recently lost her husband to the big C so I need to be careful. Every small thing is sending her into tears so when her...
Replies
16
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
701
My Tesla UMC plug gets extremely hot and then defaults to the max output of 5amps after about 20 mins. However, I tried my brothers Tesla UMC and...
Replies
1
Views
776
Hello My dear old mother tried to clean the tiles in our utility room by using a damp rag and I think some water may have dripped into our plug...
Replies
21
Views
4K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock