Discuss bad domestic installation, currently occupied in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
14
got a call from a landlord the sockets werent working , so popped round . i thought the tenant might of pretended to be the land lord in the call similar voice. old wiring in the sockets could be the problem , but it was everything else that made me ask what has happened there.
1 electric range cooker on a 20A mcb inspect cooker switch 2.5 t and e . she said electrician installed and signed off. but said dont use everything on the cooker at once
2 no sleeve on cpc sockets
3 no access to cutout , kitchen fitters had hidden it
4 no earths on lights, understandable as old wiring but electricians had been removed all pendants put up metal wall lights , even if they were class 2 they hadnt put the circuit on an RCD
5 no smokes
realising i didint go round for an EICR and if i did it would fail ,tho i was intrigued what the inside of the consumer unit was like and how the old lighting had been connected to flex just below wallpaper and not running in prescibed zone , i left
 
Those range cookers most of the time go on a 13a plug top as they are large and under powered, why people buy them I don't know, they should just get a proper oven.

20A racial for it sounds fine imho
 
Those range cookers most of the time go on a 13a plug top as they are large and under powered, why people buy them I don't know, they should just get a proper oven.

20A racial for it sounds fine imho

The full electric range classic 110 induction has a total load of 16Kw. They still work fine on the old 32A 6mm with diversity applied blah blah. I wouldn't like to say if it would hold on a 20A come Xmas though...
 

Reply to bad domestic installation, currently occupied in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
770
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, Testing question for you. I'm currently testing an existing domestic installation. The wiring is about 20-25 years old. We have rewired...
Replies
7
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
933
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top