I wonder if you can help I've just had a EICR on a property and I've received a C2 due to the fact the down-lights aren't IP rated. Having sat the BS 7671 some years ago the BS tells me that the zone 2 height is 2.25m. The ceiling in question is 2.3m. Appreciating it's advisable and I'll swap them out but is it the Regs considering it's outside the zone? Have things changed? Thank you in anticipation. Alan
 
Regardless of zoning, all items of electrical equipment need to be suitable for whatever environmental conditions they are located in.
I would say personally that lights directly above a bath will be exposed to high levels of moisture from steam, likewise with a shower they could be exposed to the water spray bouncing off the top off my bald head. Therefore I would fit IP65 or higher.
Elsewhere in the bathroom may not be as exposed to moisture and a lower IP rating might be acceptable.
Which highlights one of the issues regarding EICRs in general - the person conducting the EICR and putting his name and reputation to it is the ones who makes this kind of judgement. And one electrician will differ from another, and another.........
 
Regardless of zoning, all items of electrical equipment need to be suitable for whatever environmental conditions they are located in.
I would say personally that lights directly above a bath will be exposed to high levels of moisture from steam, likewise with a shower they could be exposed to the water spray bouncing off the top off my bald head. Therefore I would fit IP65 or higher.
Elsewhere in the bathroom may not be as exposed to moisture and a lower IP rating might be acceptable.
Which highlights one of the issues regarding EICRs in general - the person conducting the EICR and putting his name and reputation to it is the ones who makes this kind of judgement. And one electrician will differ from another, and another.........
Loz, appreciate the reply. So I believe your saying it's not necessary regulatory it's a judgement from those who carried out the EICR which I entirely agree with and will swap them out. I would have thought if it's obviously not regulatory it would have been a C3 as in a recommendation but I guess that's where the judgement comes in of the approved contractor. Thank you.
 
Welcome to the forum mate.

Depending on where the light is fitted will depend on what IP rating it has to have. This is in the regs.
Below is a screen shot of the zones.
1645470577399.png

Hope this helps.
 
Whether it's a C2 or C3 is down to the judgement of the person doing the inspection. If there is obvious deterioration of the downlights, or signs of water ingress, that may well be a C2, even if outside of any zones.
 
Whether it's a C2 or C3 is down to the judgement of the person doing the inspection. If there is obvious deterioration of the downlights, or signs of water ingress, that may well be a C2, even if outside of any zones.
I didn't appreciate it was that much down to judgement.

There is no deterioration or signs of water damage but I'll take the hit as there is potential for them to be dangerous especially if you have a bald head ; )

Thank you for your help, good to know you can get help when needed.

Best regards Alan
 
Thanks Spoon looks the same as 2008 standard so nothings changed.

Nope, nothing has changed with regards to zones.
So what IP rating is your light and what zone is it in?
 
The C2 should quote the number of the reg that has been violated. If it's the one referring to zones, then the classification is incorrect; if it's the suitable for environment one, then maybe C2.
 
C3, improvement strongly recommended.

It’s outside the zones, by all of 5cm, and degradation through insufficient IP rating could be years… depending on ventilation, how often it’s steamy etc

Is it dangerous? No
Is it potentially dangerous? Not for some time, possibly by the next EICR. By which time, any recommended improvements would have been actioned.
 

Reply to Bathroom Down-lights CODE C2? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Another accidental landlord, quite possibly another dodgy EICR? I instructed an electrician (Essex area) to perform an EICR at the house I rent...
Replies
12
Views
2K
Would be interested to know how people would code this: Upstairs bathroom - with pull cord and shower switch above 2.25 (just)... but over the...
Replies
14
Views
6K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
I've purchased Lepro 15m LED strip lights - product code PR410047-RGB-UK, and have fitted them at the top of the walls in my daughter's bedroom...
Replies
9
Views
2K
Hi all Eicr being undertaken, what code if any would you consider for this scinario Small bathroom in a flat, with airing cupboard inside, no...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock