Discuss Bathroom wiring advice in the Lighting Forum area at ElectriciansForums.net

benhurr

DIY
Reaction score
10
1. Does every powered item in bathroom needs fused spur outside?
2. Can separate RCD be required even if the supplied power is under CU RCD (for example whirlpool bath or underfloor heating)?
Please check and comment rough wiring diagram (there is no details like L N G etc, just rough requirements idea)
I am getting quotes for electricians and what to make sure they are doing the right thing. From my past experience most of a cheaper trades persons would cut a lot of corners and it result in further fixing etc.
 

Attachments

  • bathroomwiringdiagram.pdf
    48.5 KB · Views: 11
The simple answer to question 1 is no, not everything requires a fused spur, depending on the appliance other types of isolator may be necessary.
Normally a seperate isolator is not installed for lights or a shaver socket, they simply connect to the lighting circuit in the normal way.

We can't tell you how the electrician you use will do things as we all work differently and have our own way of doing things within the regulations.

The best way to avoid the cheap tradespeople cutting corners is to not use cheap tradespeople.
 
It may be worth you posting a request on here for an electrician.
there are quite a lot of us here!!
 
The simple answer to question 1 is no, not everything requires a fused spur, depending on the appliance other types of isolator may be necessary.
Normally a seperate isolator is not installed for lights or a shaver socket, they simply connect to the lighting circuit in the normal way.

We can't tell you how the electrician you use will do things as we all work differently and have our own way of doing things within the regulations.

The best way to avoid the cheap tradespeople cutting corners is to not use cheap tradespeople.
Does the underfloor heating requires separate rcd or cu rcd is enough?
 

Reply to Bathroom wiring advice in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Does bathroom light circuit required to have dedicated circuit or is it ok to be wired to other light circuits? I am getting quotes for...
Replies
4
Views
3K
Hi everyone, please advice and comment on the attached wiring diagram for a kitchen. There are mixed opinions on the need for FSU-s and number of...
Replies
52
Views
4K
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
I'd like to find a timer switch, in a style that looks alright next to decora light switches, to control a bathroom fan. The bathroom fan...
Replies
1
Views
916
We have had builders in, who have stopped for Xmas. My daughter tried to do a wash. The wash machine wouldnt. Its power socket is dead. I...
Replies
4
Views
652

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock