Octopus

All,

Being very lazy (long day after long day). Got a customer who wants 2 more 2 gang sockets and the first one "moved". The only way I think I can achieve their wishes would be to change an existing 2 gang socket (in the wall) to a FCU.

I'd rather not take the back box out and fit a dual box - so my question is, is there such a device/plate/unit available to do this.

Thanks
 
If you are feeling "very" lazy you could always plug a 6-way wall-mounted trailing socket into the original. 13amp protection which is what you wanted plus 6 sockets somewhere away from original. Sorted :cheesy:
 
Take the separation plate out of a dual accessory box and tap a hole in the centre of the plate and at the appropriate place in the double back box. thread the plate 25mm onto the bolt and then screw into the back box.
The plate will not be very solid left to right but this would be held by the accessory. Probably less effort to remove the back box!
Use an angle grinder to take off three sides of a single box to leave a flat plate and one side screw the plate into the bottom of the unused side of the back box.
*Stop thinking now Richard.*
 
All,

Being very lazy (long day after long day). Got a customer who wants 2 more 2 gang sockets and the first one "moved". The only way I think I can achieve their wishes would be to change an existing 2 gang socket (in the wall) to a FCU.

I'd rather not take the back box out and fit a dual box - so my question is, is there such a device/plate/unit available to do this.

Thanks


Sounds more like preparing a quotation to compete with a cowboy lol :D
 

Reply to Being lazy 2g to 1g convertor in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
571
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
I'd appreciate the wisdom of the find minds here regarding this job. Yes, I've drifted into Wales again.... An extension is being planned as...
Replies
4
Views
940
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I have a customer who lives in a grand old house which suffers from damp. The ground floor sockets (2 different circuits) IR test at around...
Replies
21
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock