Discuss Best RCBO CU? in the Electrical Tools and Products area at ElectriciansForums.net

W

WPD Lad

Hi all,

Wondered if I could pick your collective brains, I'm possibly looking to install an RCBO only board on my newly re-wired house and wanted to know the best make/model? I'll then weigh up the options of dual split rcd with 2 RCBO on the unprotected side or full RCBO.

Cheers
 
Hi all,

Wondered if I could pick your collective brains, I'm possibly looking to install an RCBO only board on my newly re-wired house and wanted to know the best make/model? I'll then weigh up the options of dual split rcd with 2 RCBO on the unprotected side or full RCBO.

Cheers

Can't recommend any specific boards for you, as i don't know what's available these days in the UK. What i will say, is go for an RCBO board every time, you'll not have a fraction of the problems associated with dual split RCD boards.... Those things are a cheap alternative to doing things properly, and you can pay dearly over the years, for taking that cheap route!! lol!!
 
but is it newly rewired except for the CU?
 
I use wylex although they can be quite tight for space, but look neat when dressed in well. RCBO's about £15 - 18. I like Hager but use Wylex as they are IMO good mid range brand and breakers easy to buy B&Q if in a jam after 5.30!
 
Silly question maybe, but if your property is newly rewired why hasn't it got a shiney new board?

Most of the first fix wiring is in but I've not made my mind up on the CU yet, house is miles off being liveable so I've got a while to make my mind up, just wanted some opinions on brands. Thanks for all the replies
 
I dont do domestic much but came across an MK sentry C.U. the other day 16th edd split board LOADS of room up top absolutly heaps

Im lookin at fitting nice shiney new C.U. in the house and Im looking at the RCBO route but Im seeing about a M.G. 1ph as they have Hunners n Hunners of room
Fittted a newlec C.U. other day 17th edd n thought to my self " theres not much room once you have all those cross split board connections flying all over the place SURLEY there is a better way to do this As for the bussbar at bottom n having to remove it to fit an MCB give me switchable M.G. every day no need to kill full db to change,add a circuit
 
These are my proposed circuits?

32A Upstairs Ring32A Downstairs Ring
32A Kitchen Ring
6A Upstairs Lighting
6A Downstairs Lighting
16A Fridge Radial
16A Freezer Radial
20A Oven Radial
20A Oven Radial
32A Hob Radial

Overkill? All on RCBOs
 
Yes Hager for sure. In about 7 years of using almost nothing but Hager, I have never seen a faulty bit of kit yet, even after years of (ab)use.
I have had other cheap RCD units that don't meet disconnection times straight out of the box !!
 
Hager definately. Where are people getting the RCBO's for 18.00 I'm paying £22???

If you want cheaper but reasonable quality the Curve RCBO boards by Denmans are good value for money and not much more expensive than a dual split RCD board
 
Bump (and hijacked?), would also be interested in going the majority RCBO route but the best prices I can get are still early 20s plus Vat.

I occasionally order from TLC and have used their Contactum boards in the past but nobody here rates them too highly (I find their boards easy to work and spacious considering they're pretty small), is it the same case with their RCBOs (18.99 web price)?
 
hi all, have a similar problem..... would like to choose an RCBO consumer unit but am confused as to which brand to use :( even on here everyone seems to have their own preference as to which one is best!
project:- just bought a soon to be 8 bedroom house with one section of the house to be letted out. this letted out section of the house will consist of 1 bedroom, 1 living area, kitchen, and a shower/toilet. The shower will "not" be electric, and will be plumbed into the house plumbing.
The hobs will be gas, the ovens will be electric in both kitchens.
There will also be 2 immersion elements in the megaflow cylinder.
The property will also have an out-building (office) with an airconditioning unit.
Can someone tell me if i go down the route of using RCBO does that mean that it "replaces" the need for RCD's on the CU?
i was thinking of using 2 CU's one for my side of the house and the other for the flat to be letted out. Is this necessary or can i just get a say 20 way RCBO board for the whole lot?.... i know one of my neighbours with exactly the same lay-out had 2 CU's put in for this same purpose, and a seperate isolation unit also installed for their out-building.
i need to use the rolls royce of CU's so pls help, many thanks in advance :)
 
Last edited by a moderator:
Can someone tell me if i go down the route of using RCBO does that mean that it "replaces" the need for RCD's on the CU?
Yes, an RCBO combines the functions of an MCB and an RCD. If you go down this route, you will need to fit an RCBO in each position that you would otherwise have fitted an MCB. It's the "best" solution for various reasons, but more expensive than RCDs and MCBs.

i was thinking of using 2 CU's one for my side of the house and the other for the flat to be letted out. Is this necessary or can i just get a say 20 way RCBO board for the whole lot?
You can do either, but think about the situation if an MCB feeding a circuit in the flat trips and the occupier wants to reset it when the part of the building containing the CU is unoccupied. Also, if you ever want to meter the consumption of the flat separately, you'll need to have two CUs.
 
handysparks.... i didn't know you could have 2 meters fitted as i'm sure a few years back i made an enquiery to the electricity board and i'm sure they said that we couldn't as it was the same dwelling! also what about all the other elements i have listed? i.e.... 2 emmersions,2 ovens, out building, etc. pls advise, many thanks in advance :)
 
Went into a local denmans and they're selling Curve RCBO boards for £82+Vat (iirc ~10 way box, 6 rcbos and main switch). Box is designed for rcbos too so would of been a easy fix if we didn't buy one just for the breakers. Next CU change I may opt for another one to try out
 
handysparks.... i didn't know you could have 2 meters fitted as i'm sure a few years back i made an enquiery to the electricity board and i'm sure they said that we couldn't as it was the same dwelling! also what about all the other elements i have listed? i.e.... 2 emmersions,2 ovens, out building, etc. pls advise, many thanks in advance :)
You can have two supply meters if you have a second supply to the building (at a cost). Or you can fit a private meter to the supply to the flat and use it as the basis for charging for the electricity used (there are rules about how much you can charge).

As far as the rest of the design of the installation goes, you'd be best discussing it with an electrician who can see the physical layout and spend time on a design. Someone on here may be local to you. Where abouts in the country are you?
 
Re: Best RCBO NHP

Without a doubt the best RCBO is the NHP MOD6.
I've been installing RCD safety switches exclusively for 13 years in Australia using exactly the same gear that is used in the UK and Europe.
Without a doubt the best RCD RCBO safety switch is the NHP MOD6 which I've now been using for several years. It is made in Hungary, although even if it was made in China it would probably make little difference? It is the only RCBO that has never let me down so the Quality Control must be right up there. The MOD6 is also branded by several other big electrical manufacturers as it has proved so robust.
R Middleton
SafetySwitch electrical services
Perth.
 
contactum for me. old school look and metal enclosures. made in uk not some chinese crap. fair prices on rcbo and accesories.
 
The only rcbo's I now use are supplied by SBS.
They are single module and double pole, so no neutral fly lead to mess up the enclosure. They are space saving being single module and utilize a dual busbar.
£13.00 each.
 
Id go for the rcbo everytime forget the split loads CU's you really dont want the issues of nuisance tripping, i have a contact who has been importing the standard rcbo units which are made at the same factoty as the contactum range which cost £10 plus vat which fits the MK boards or his own IP55 rated boards

he also does the new compact rcbo units which are the same 19mm width and the same height as a standard mcb unit for £12 plus vat, i got a 12 way IP55 rated CU with 100 amp main switch, eight compact rcbo's with two free spaces for expansion, delivered next day inc vat for £144.00

lee
 
+1 with not clever my supplier is "david stansfield" "SBS" great guy great products

"amlu" think if you look into contactum a little deeper their rcbo's are made in china same as MK

lee
 
Last edited by a moderator:
He told me he used to be a napit assessor, I must give him a call I need a couple of boards for a job in a week or so......might need some of his new lamp post rcbo's/timer units if customer accepts my quote.
 

Reply to Best RCBO CU? in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
778
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
Replies
55
Views
4K
Have an existing old client with what's best described as a sprawling small-holding of a property. There's an armoured external supply which...
Replies
25
Views
3K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
771
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock