Discuss Best Relay for a Motor in the UK Electrical Forum area at ElectriciansForums.net

N

Neil Scrivener

Hi Guys,

I have a 'garage' style electronic hoist.

An example of the type is: Hilka Pro-Craft 500kg Electric Hoist | Workshop Equipment | NoLinkingToThis

As you can see there is a two position switch, and inside there are some capacitors for starting voltage. The Switch on one 'side' is Live, and the other 'side' Neutral.

What I'm looking for is to replace this switch with a Relay, so that I can control this from a distance over Low Voltage (ie 12-24V).

I'm happy with all the principles of the wiring, but wondered what anyone can recommend in terms of a Relay that would be be a suitable replacement for a switch?

Cheers
Neil
 
i'd be wary of modifying it for safety reasons. also, if anything untoward happened, the manufacturers would disclaim any liability.
 
To really give an answer we need a bit of info -

-What voltage is the motor and how many phase (I assume 230v single phase here as you mention starting cap's)?
-Is the switch motor load bearing or just a low load control circuit?
-You say your OK with the wiring side so are we to assume you are knowledged in the BS60204 which will cover how you go about doing what you wish, as you will have to consider some form of electrical and mechanical interlock to ensure you cannot by operational error or electrical/machanical failure have the motor been told to go in both directions. (this can be achieved with a mechanically interlocked F/R contactor set up).
-Your safety system will also need extending if the pendant isn't been used, if you are adding additional actuation points to the existing this may mean you change the requirements of the control voltage and the protective measures like an isolating transformer may need to be incorperated.

What at first seem a simple adaption becomes a little more costly, these existing controls are often designed to fall below certain requirements and are made very simple but the act of adding or extending these systems can often change the requirements of the original controls thus make them non-compliant.

 
Last edited:
Your safest bet here is to just extend the existing pendant to the required length, you will still invalidate the warranty and put all responsibility on your shoulders as the designer of the control circuit even if its just to extend it...(if someone is injured or worse by this equipment, you will need to show that any alteration you did did not compromise the safety of the equipment and more so, complies to the current regulations) also to add just for your own clarity here is Low Voltage is what I assume the controls are already (230v), 12-24v is classed as Safety Extra Low Voltage, these minor descriptive errors are why I ask if your knowledged with the EU Low Voltage Directive namely the BS60402 as their is a section of this that covers the requirements of lifting equipment and cranes etc as well as the general requirements for the control side.. together they have a bearing on what you are and are not allowed to do here, like has been said, its not just as simple as making a functioning control circuit and incorporating it to the existing.
 
Last edited:
Your safest bet here is to just extend the existing pendant to the required length, you will still invalidate the warranty and put all responsibility on your shoulders as the designer of the control circuit even if its just to extend it...(if someone is injured or worse by this equipment, you will need to show that any alteration you did did not compromise the safety of the equipment and more so, complies to the current regulations) also to add just for your own clarity here is Low Voltage is what I assume the controls are already (230v), 12-24v is classed as Safety Extra Low Voltage, these minor descriptive errors are why I ask if your knowledged with the EU Low Voltage Directive namely the BS60402 as their is a section of this that covers the requirements of lifting equipment and cranes etc as well as the general requirements for the control side.. together they have a bearing on what you are and are not allowed to do here, like has been said, its not just as simple as making a functioning control circuit and incorporating it to the existing.

For clarity, darkwood meant to type 60204, rather than 60402. Everything else is spot on, it might look simple, and no doubt you can get something working, but one day your circuit might not work as you expect. Then somebody might get injured.
 
Hi Guys,


Sorry I should explain who I am, and what I do better.



I work usually in music touring - I set up very large stage lighting rigs in Arenas all over the world for bands/artists, probably well known to you - and spend most of my time dealing with multiple 400A Three Phase supplies, and distributing them over hundreds of lights. So I'd like to think I am more than competent in the re-wiring of a small project as simple as this :)



Part of my job is using CM Lodestars (check them out) which use a 24V Control Voltage, so I know pretty well what the end result I'm looking to achieve is. In this regard, I am fully familiar with the Health & Safety regs that need to make this compliant - perhaps more so, because in my industry motors sit above an audience of several thousand, or a band worth several million!



The Motors are single phase, have 13A Plugs, so that's really easy, I can do that bit with ease!



The reason why we want to put this relay system in is because 4 motors will be mounted on a test truss, and for safety I need to be able to control them all at once, as obviously if you don't run them simultaniously, the weights change per point, and so forth.



Basically I want to use relays; somehow, replace them with the switch - and then there will be a low voltage hand controller with 4 switches and a 'go button' which will control each motor depending how (or not) the switch is selected.



The concept, I do every day quite simply, we have off the shelf products that do this (google Outboard Electronics) - I just need to convert these particular motors for this purpose - and the off the shelf products in our industry are not compliant with how the motor appears to be wired, or within budget.



Cheers

Neil
 
Thanks for the update, the area of work you are in explains your mix-ups with the terminology we use everyday and you probably don't.

If your happy and well versed in the relevent regulations and H&S requirements then I'll not preach the mountains of regulations to you anymore...

I would require a wiring diagram of the motor/control to advise correctly, but basically you have a raise and lower option you need to extend and mimic with a contactor arrangement, also because the existing switch operations prevent mechanically the chance of the motors raise and lower option been chosen together you will need to do this with contactors - you can get a Forward/Reverse pre-arranged contactor with mechanical interlock to prevent the motor been called to go both ways be it through error or failure of parts, also using auxillary contacts to give electrical command isolation too.(Fail safe)
 
I also work as a production electrician/lx tech/rigger/fly man but that doesn't qualify me for jack-sh*t in terms of motor control wiring.
You're now in the territory of the low voltage directive and the machinery directive whereas rigging is normally more in the realms of loler and puwer
 
Darkwood, I'll have a dig around next week and send some pictures :) probably won't be until next week.

With respect, Davesparks, I think you've missed the point - with respect, our outlook in the side of the industry we work in may be a little different from a theatrical one :)
 
With respect, Davesparks, I think you've missed the point - with respect, our outlook in the side of the industry we work in may be a little different from a theatrical one :)

What is the point then?

The chain hoists used in all parts of the entertainment industry are the same, just industrial units painted a different colour. They all turn up as plug and play units with the control systems pre-built with all the electrical safety considerations taken care of.
The closest you get to any controls wiring is if you are installing the hoists permanently when you get a wall mounted control panel rather than a rack mount one.
 
The point is, this item is purely for a testing area; not to be used in a 'live' environment on site.

The users of this machinery are fully competent to use it. Likewise, we as a company (who own 40+ motors in production/rental stock) have fully competent personnel who are capable of the wiring - we build our own mains distribution up to 400A, as well as manufacture various cables for clients. We have personnel that can sign of to BS7909, BS2395 etc - this specific area is simply out of our typical scope of work, but it doesn't make us stupid. I presume as a ''rigger'' you hold an NRC :)?

What you say about installed Hoists is, with respect, irrelevant. Installed motors, as perhaps you know will tend to be 3 phase Direct Control (ie switching the phasing) - or in some occasional cases LV control. This is some lightyears away from what the hoist in question is, and in any event DC or LV 'bog standard' controllers would not work for this application.

We are simply looking for some advice on an alien (to us) area of electrical world, hence I joined up to see if we could find some sensible assistance. With respect, I feel the need to plead the case of competency more than actually get to grips with the nitty gritty of the original question.

For the sake of sensibility, could we kind of move on from the concept that there is an element of 'danger' involved? I assure you we have fully scoped this area....
 
I'm not familiar with BS2395, what does that cover?
Being a testing area is irrelevant, the exact same legislation covers the machinery controls, emergency stopping etc.
Actually I think all of the installed systems that I've fitted have been elv controlled as it allows limit switches to be used.
I would have thought a setup similar to the bog-standard controls would be best for your application as you will presumably still want the individual control for levelling? You could imitate the standard setup completely with an elv transformer and relays at each motor connected back to some yellow commando sockets, then you'd be able to use your existing elv controllers or build a little panel for it.
Or else you'd need the same relays at the motor but with the elv source in the panel.
But either way the e-stops are presumably going to be cutting the supply to the motor?
I think your original question was about relays, any standard industrial relay with the right coil voltage and a contact rating at least equal to that of the switch currently used should do the trick.
 
Hi Guys,

I have a 'garage' style electronic hoist.

An example of the type is: Hilka Pro-Craft 500kg Electric Hoist | Workshop Equipment | NoLinkingToThis

As you can see there is a two position switch, and inside there are some capacitors for starting voltage. The Switch on one 'side' is Live, and the other 'side' Neutral.

What I'm looking for is to replace this switch with a Relay, so that I can control this from a distance over Low Voltage (ie 12-24V).

I'm happy with all the principles of the wiring, but wondered what anyone can recommend in terms of a Relay that would be be a suitable replacement for a switch?

Cheers
Neil


Sorry to be a sad nitpick, but this is Extra low voltage.

:rolleyes2:
 
We are simply looking for some advice on an alien (to us) area of electrical world, hence I joined up to see if we could find some sensible assistance. With respect, I feel the need to plead the case of competency more than actually get to grips with the nitty gritty of the original question.

For the sake of sensibility, could we kind of move on from the concept that there is an element of 'danger' involved? I assure you we have fully scoped this area....
We are not questioning your competence in your own area of work but by your own self admittance you are trying to do work that takes you into a totally different area of legislation and regulation, we are trying to point this out to you, regardless of motors been 1ph, 3ph AC,DC etc the very act of trying to alter or combine control for multiple motors will mean you have to comply to other regulation you're probably unaware of, of which we are trying to advice you, I have already hi-lighted certain criteria you may need to meet but from your explanation I believe you would be required to intergrate a critical safety circuit common to all motors, electro/mechanical interlocked directional controls, possibly a global monitoring system to ensure like you say that load is kept balanced.
We lack so much info here to give tailored advice tbh but from what you have given it does strongly lean towards the need to meet the EU Low Voltage Directive and as already mentioned you will be falling under the 'Safety of Machinery - Electrical Equipment of Machinery'.

We are not trying to trip you up here, the manner of you question and what you want to achieve all point to a need for you to comply to the suggested regulations, the area you work in, be it stage lighting for a concert to production line machinery is irrelevant here, they all have to comply to the same regulations when designing the control systems.

When we bring up this subject you repeatedly reply you are competent and fully aware of the regulations you have to comply to yet this does not show in your replies and the actual questions you are trying to ask... if you are linking these motors together to a common control system you effectively alter the requirements the original motor controls were built to and makes them non compliant - you cannot simply extend the control of 4 seperate motors hoists to a common control system (yes that is simple in theory and practice and probably would work, but falls far short of requirements.)

All we are doing by dragging this out is to ensure you are aware of the correct regulations you have to adhere to, so far you have not shown this in your replies. We want to avoid giving misleading advice here so with all respect to the knowledge you have in your own field, we are asking you to realise you maybe entering a whole different level of your work to that which you are used to.
 
Last edited:
Isn't it strange that similar threads appear on other sites and once rebuked the OP moves on until someone gives them what they want to hear
 

Reply to Best Relay for a Motor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K
So this is a question around my woodworking workshop. I have a dust collector which is connected up to various machines around the shop and want...
Replies
3
Views
719
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hey, I've been asked a question 'what are operational systems on Transistor H-bridge system for a conveyor motor with speed control property's'. I...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock