Hi

I'm installing two new sub-mains. I need to parallel some of the supply cables.

It's the main incomer in 5 x 25mm, with 5 x outgoing 25mm tails to the adjacent DB, and an outgoing 4-core 35mm SWA going off to another building a long way away.

I will terminate in a 300 x 300 x 75mm metal box. What would others use to make the connections inside this box?

I thought about line taps screwed to the back plate, or five of these tails blocks. But if feels a bit unwieldy. Is there a better way?

Thanks, Mark

proteuscon_etb5br.jpgproteuscon_etb5gn.jpg
 
I would normally prefer to put a distribution board in.
 
Don't you want and/or need (a) some means to isolate each supply, and (b) some form of OCPD or fault protection for the longer sub-main?
 
Thanks. I didn't explain this well.

The incoming 5 x 25mm runs from a 3P 50A MCB in the main DB at the origin. That protects this cable, and anything else (so long as the CSA is big enough) downstream, without further protection. I dislike cascading MCBs for multiple sub-mains as it's usually impossible to provide discrimination.

And there are already 11 DBs in this install - which is my own house and workshops - and I don't want any more!

But ... there is already a DB (Hager 3P 12-way) next to my proposed joint box, to be run from the outgoing 25mm tails.

I really don't want to ram two heavy cables into the supply side of that DB's main switch, even using crimp tags, as that little 100A switch is not designed for it; and taking the 35mm lines out from yet another MCB would be, in my opinion, poor practice.

Effectively I'm running the two downstream sub-main DBs from the one 50A mcb in the main board. How is that different from running from a bus bar chamber? I just want a simple solution.

My question was how best to terminate. I'm a bit rusty, and there may now be connectors I've never heard of.
 
If you are looking at 35mm/25mm paired in to a 100A switch then yes it is a bit of a tight fit.

If you are looking at using a DIN box then you can get terminals for it that have bolts so doubled-up lugs are an option, for example:

You also get terminals that can be paralleled, so 2 * 2-way for 4 cables, for example:

You can also get DIN mounted distribution not unlike the Henley blocks as well, but not always for 35+25 sort of splits:
 
Six months later I got around to finishing this job, as digging 200m of trench did not fill me with enthusiasm. I eventually rented a chain trencher which I'd not used before. It's a marvellous piece of kit, highly recommended.
Thanks for the suggestions, but in the end I screwed four 35/25mm line taps to the box, run the uncut 35mm through and piggy-backed the 25mm on top. It's analogous to an underground branch.
I think it worked well, was simple, and reduced the number of joints.
To recap, this is downstream of a 3P 50A MCB, and is to run two DBs, one local, one 200m away.
I'm posting this conclusion for completeness, and in case this is useful to others. Plus I'm sure some will enjoy telling me I'm wrong, the job is rubbish, and it doesn't comply with some regulation or other. Carry on :) .Line taps.jpg
 
Last edited by a moderator:
Looks like a neat solution
as long as those terminals are rated for over 50A (would be amazed if they are not) then it all gets a thumbs up from me.

however if you are really looking for criticism, why can I see a hole to the right of the left hand cable entry?
 
however if you are really looking for criticism, why can I see a hole to the right of the left hand cable entry?
Well spotted! Looks like 20mm gland in 25mm punch-out?

Given the earthing nut and decent flying lead to it I guess the only issue us if it is not able to stop the gland pulling away, but that seems unlikely.

A few spare banjos might have hidden it!

EDIT: Realised it must be bigger then 20mm/25mm for that cable size, doh!
 
Last edited:

Reply to Best way to parallel 25mm/35mm singles in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi. I have some TP supply SPD and JB to re wire in 25mm TRI rated cable this weekend. For the Iine conductors i am using 35mm DIN connectors...
Replies
12
Views
2K
There’s been a few recent threads about caravans, caravan sites etc, and I thought I’d post up some photos I took today while on one such site...
Replies
0
Views
900
Hello all. 17th edition sparky here, but not been on site for the last 3/4 years (had a bit of an accident). Just bought a house with a 16mm 3...
Replies
15
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock