Discuss Best way to step up voltage for electric motors in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
1
We've been tasked to run power to some electric motors on some pumps and the building is currently 120/208vac 3ph. The motors are 230/460vac 3ph. Instead of getting new motors that run on 208vac, they're asking if we can get a transformer to step up the voltage from 208vac 3ph to 240vac 3ph. The 120/208 panel that is currently installed in the warehouse area is a 400 amp service that is basically empty, so we have plenty of power to handle this. It would be a total of (3) of the pumps listed below on (3) separate holding tanks.

Motor Info:
Lesson Ultimate E
Model: C254T1FK1
230/460 3ph
15hp 11KW
F.L. Amps - 37/19
PF - .82

Our initial idea was to come from the 400 amp panel to a step-up transformer -> sub panel -> motor starter -> contactor -> disconnect -> motor.

Given the above info, could someone recommend a good set up to make this work. We've talked to the supply house and they're telling me there isn't a step-up transformer to go from 208-240, that we would have to use several buck boosters to try and accomplish this. They also mentioned reverse wiring a 240-208 transformer (120 on the secondary to get 240 on the primary); I haven't done this before, so any info would be very helpful.

If the scenario above is too difficult, doesn't make sense, or is too costly, we still have the option to step up to 480vac 3ph, which I can get a transformer for this pretty easy, but the customer is wanting a quote to do it both ways.

Thanks in advance
 
a 2:1 tranny would give you 240/415V which is a standard voltage. the european version is 230/400V.
 
If there's several large motors we'd usually install a separate motor control panel to house the switchgear, drives, interlock contactors etc with a built-in supply transformer and supply all the motors from that panel. Basically an MCC/PCC combo. Usually the transformer would be 480V which is good for running 460Volt NEMA motors
 
Last edited:

Reply to Best way to step up voltage for electric motors in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi there im in training, but my question is using using a 3 phase 480v delta to 208/120 delta transformer 30kva and wiring it in reverse for 208...
Replies
1
Views
714
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
489
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
The machine is a Sunnen CK-21-E used for Honing. I cannot find any manuals but ill post the tag. I dont believe its multi-voltage which would make...
Replies
5
Views
2K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
770

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock