Might be hard to tell now, but what were the terminations like?
im thinking these were all fitted when the block was new, just wondering if maybe the same- not very effective- electrician did the connecting and left a loose screw in these particular flats.

clutching at straws, but always something to think about if all other avenues of investigation are exhausted.
 
Might be hard to tell now, but what were the terminations like?
im thinking these were all fitted when the block was new, just wondering if maybe the same- not very effective- electrician did the connecting and left a loose screw in these particular flats.

clutching at straws, but always something to think about if all other avenues of investigation are exhausted.
Has to be a factor.... The ability for someone to just make a mistake/miss something is super high
 
I would also see if the affected units are on the same phase still can’t rule out floating neutral
If love to, I fact already discussed the possibility with site but that is a herculean task without drawings, access and someone on site who has a clue.
 
Might be hard to tell now, but what were the terminations like?
im thinking these were all fitted when the block was new, just wondering if maybe the same- not very effective- electrician did the connecting and left a loose screw in these particular flats.

clutching at straws, but always something to think about if all other avenues of investigation are exhausted.
Possible but it's the time frame that leads me away from workmanship, coupled with the recent other electrical issues.

I don't know for sure but the block looks to be ten year old and for bad workmanship to start to show up so late in the day then all within a week makes me think other factors are at play.
 
Here's some photos @Lucien Nunes and others.

The terminals and cables are clean as a whistle.
20210820_172348.jpg


This is the culprit

20210820_172324.jpg


Capacitor(?) has blown.
16294772800054135938986441041712.jpg
 
They are rated at 16A. The hot water cylinders are on a dedicated circuit off their own 16A MCB, isolated via a 20A double pole switch, length is a couple of meters.

Couldn't see a rating on the element but looking into that now.

Edit to add,

The elements are 3kW but looking at the plumbing I think they're on a central hot water system as there seems to be a coil on the cylinders.

I'm back there tonight two replace a couple and grab some more info.
Would definitely clamp it , you may get over 14 Amps if lucky...lol but is stuff that good nowadays. BTW i only use Timeguard products for this type of stuff as fed up changing crap out after a few years
 
Looks like a metal oxide varistor connected across the supply, If several blew at once this is a sure sign of overvoltage on the supply. A MOV is normally high resistance, but it's resistance drops as the voltage increases to stop voltage spikes. A sustained overvoltage such as from a supply fault will quickly overheat and destroy an MOV.
 
Looks like a metal oxide varistor connected across the supply, If several blew at once this is a sure sign of overvoltage on the supply. A MOV is normally high resistance, but it's resistance drops as the voltage increases to stop voltage spikes. A sustained overvoltage such as from a supply fault will quickly overheat and destroy an MOV.
Would definitely put my money on a floating neutral as some stage some Dno have a search function on there site to advise if there have been any incidents in the locality
 
Yup, it sure does look like an MOV that wasn't big enough absorb the available energy in the overvoltage event. When that happens, it can initiate an arc that lasts until the fuse blows, which can dissipate so much more energy that it makes it hard to identify whether the trigger event was an impulse or a prolonged excursion above clamping voltage.

Assuming the building is served by conventional urban underground distribution the latter seems the most likely and I would say the likelihood of a cable fault causing both the timer damage and the flickering / outage events was very high. Other items in the properies with MOVs (and even SPDs) might also have been compromised, but if the MOVs in the timers had a slightly lower clamping voltage then they might have all gone phut before many of the remainder showed signs of distress.

The sub might be specific to the estate or building, in which case any information you can get from the DNO about recent faults might nail it.
 
My thinking of what we have so far.

The catastrophic failure or the MOV (thanks) in the controller would point to a large over voltage situation.

It is most probably not environmental but a lost Neutral.

Without further information this could be anywhere internal or external.

So I was thinking to approach it on two fronts, to contact the DNO and report a possible Neutral fault whilst surveying the site, reported faults and drawings to see if a pattern can pinpoint the location.

So in a normal fault free situation the installation should look like.
20210821_084103.jpg


If the fault is in the below position then I should only be hearing of power outages in flats 7, 8 & 9 but not over voltages or the MOV failures I'm seeing.
20210821_084130.jpg


If the fault is in the below position then flats 4, 5 & 6 and flats 7, 8 & 9 will see voltage fluctuations between 0V and 400V depending on their respective loads, this situation could cause the MOV failures.
20210821_084146.jpg


And finally, in the below image the fault would be evident across all phases and all flats with under and over voltages. Whilst there are sections of the internal installation that could contain the fault; in this scenario the fault could also be external.
20210821_084200.jpg


Ii actuality I have already informed the client of the liklihood of a serious fault existing and that it may be internal or external and they will be picking it up from here.

I'm quite disappointed really as its quite interesting to see how far you can fault find on paper if you have enough information.
 

Attachments

  • 20210821_084130.jpg
    208.2 KB · Views: 3
Your explanation of the possible scenarios is correct but the configuration in pic.3 is unlikely to exist in practice. Each single phase service will be derived from a 3-phase busbar, with neutrals normally serving one or three phases but seldom two.

If the fault was a cable strike, the neutral may have not merely been broken but also shorted or arced over to a line. A variety of different voltages may have been impressed on the loads in quick succession as the fault developed.
 
I don’t think the burned out disc is an MOV. The timer uses a transformer less way of producing low voltage dc to operate the electronics. I reckon one can see a bridge rectifier - the white block component, and a disc capacitor in series with a resistor of suitable power rating together forming a mains to low voltage dropper. The placement of the resistor and the disc capacitor makes me think their right hand ends are connected to Lin and Nin respectively and their left hand ends to the ac inputs of the bridge rectifier which are normally the inner two leads for this style of rectifier. There is a smoothing capacitor to the left of the bridge rectifier. I reckon the gold rimmed cylindrical component above the relay is a battery for keep alive in the event of power cut and accumulator to handle short duration current surges when the relay turns on.
 
Last edited:
I don’t think the burned out disc is an MOV. The timer uses a transformer less way of producing low voltage dc to operate the electronics. I reckon one can see a bridge rectifier - the white block component, and a disc capacitor in series with a resistor of suitable power rating together forming a mains to low voltage dropper. The placement of the resistor and the disc capacitor makes me think their right hand ends are connected to Lin and Nin respectively and their left hand ends to the ac inputs of the bridge rectifier which are normally the inner two leads for this style of rectifier. There is a smoothing capacitor to the left of the bridge rectifier. I reckon the gold rimmed cylindrical component above the relay is a battery for keep alive in the event of power cut and accumulator to handle short duration current surges when the relay turns on.
A picture of the underside of the PCB would be handy.
 
The white block will be the dropper capacitor, the bridge rec will be SMD. But yes, let's see some pics of the PCB
 

Reply to Block of 200+ flats, eleven single channel hot water timers blown this week alone. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I am currently in the process of estimating the electrical demand for a new construction development that will consist of an...
Replies
0
Views
819
Need help with a quote here. I’m wanting some sound advice. Was called out to the hot water not working so repaired the issue within the panel...
Replies
10
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
814
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
423
Hi everyone, I need some help with an electrical issue I'm experiencing. I recently created a new circuit for an electric oven at my friend's...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock